Network Management Card AOS v6.4.0 Galaxy VM Touch Screen APP v6.4.1 NMC Serial Number: ID1439000780 Date Time Name Contact Location System IP 03/26/2025 15:33:50 UPS 1B COTEL SAS CUARTO ELECTRICO 172.17.3.131 Date Time User Event Code 03/26/2025 11:58:26 Device UPS time has been changed. 0x3790 03/25/2025 16:18:23 Device Modular battery cabinet 2 is ok. 0x37EE 03/25/2025 16:18:23 Device Modular battery cabinet 2 breaker 2 is closed. 0x37CE 03/25/2025 14:33:44 Device Modular battery cabinet 2 is not working correctly. 0x37EF 03/25/2025 14:33:44 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 03/25/2025 14:33:16 Device Modular battery cabinet 2 is ok. 0x37EE 03/25/2025 14:33:16 Device Modular battery cabinet 2 breaker 1 is closed. 0x37CE 03/25/2025 14:22:32 Device The UPS is charging the batteries. 0x37E7 03/25/2025 14:22:22 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 03/25/2025 14:22:22 Device Charge voltage is set to float voltage level. 0x375C 03/25/2025 14:22:22 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 03/25/2025 14:22:22 Device Surveillance OK. 0x3780 03/25/2025 14:22:21 Device The UPS is ready to enter static bypass but awaits permission from the system. UPS output is off. 0x3758 03/25/2025 14:22:21 Device Charger is off. 0x3765 03/25/2025 14:22:21 Device Surveillance detected fault. 0x3781 03/25/2025 11:58:27 Device UPS time has been changed. 0x3790 03/25/2025 11:40:49 Device Modular battery cabinet 2 is not working correctly. 0x37EF 03/25/2025 11:40:49 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 03/25/2025 11:39:57 Device Modular battery cabinet 3 is ok. 0x37EE 03/25/2025 11:39:56 Device Modular battery cabinet 3 breaker 1 is closed. 0x37CE 03/25/2025 09:18:06 Device Modular battery cabinet 3 is not working correctly. 0x37EF 03/25/2025 09:18:06 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 03/24/2025 11:58:27 Device UPS time has been changed. 0x3790 03/23/2025 11:58:27 Device UPS time has been changed. 0x3790 03/22/2025 11:58:27 Device UPS time has been changed. 0x3790 03/21/2025 11:58:27 Device UPS time has been changed. 0x3790 03/20/2025 11:58:26 Device UPS time has been changed. 0x3790 03/19/2025 11:58:27 Device UPS time has been changed. 0x3790 03/18/2025 15:33:29 Device Modular battery cabinet 1 is ok. 0x37EE 03/18/2025 15:33:29 Device Modular battery cabinet 1 breaker 2 is closed. 0x37CE 03/18/2025 13:53:04 Device Modular battery cabinet 1 is not working correctly. 0x37EF 03/18/2025 13:53:04 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 03/18/2025 11:58:27 Device UPS time has been changed. 0x3790 03/17/2025 11:58:26 Device UPS time has been changed. 0x3790 03/16/2025 11:58:27 Device UPS time has been changed. 0x3790 03/15/2025 11:58:27 Device UPS time has been changed. 0x3790 03/14/2025 11:58:26 Device UPS time has been changed. 0x3790 03/13/2025 14:46:46 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/13/2025 14:46:37 Device Communication between Main Controller and display is fine. 0x370B 03/13/2025 14:46:13 Device Main Controller is unable to communicate with the display. 0x370C 03/13/2025 11:58:27 Device UPS time has been changed. 0x3790 03/12/2025 11:58:27 Device UPS time has been changed. 0x3790 03/12/2025 11:52:12 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/12/2025 11:52:02 Device Communication between Main Controller and display is fine. 0x370B 03/12/2025 11:51:38 Device Main Controller is unable to communicate with the display. 0x370C 03/12/2025 11:45:47 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/12/2025 11:45:37 Device Communication between Main Controller and display is fine. 0x370B 03/12/2025 11:45:13 Device Main Controller is unable to communicate with the display. 0x370C 03/12/2025 11:42:06 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/12/2025 11:41:57 Device Communication between Main Controller and display is fine. 0x370B 03/12/2025 11:41:33 Device Main Controller is unable to communicate with the display. 0x370C 03/12/2025 10:40:07 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/12/2025 10:39:57 Device Communication between Main Controller and display is fine. 0x370B 03/12/2025 10:39:32 Device Main Controller is unable to communicate with the display. 0x370C 03/12/2025 08:07:17 Device The UPS inverter output is in phase with the bypass input. 0x3721 03/12/2025 08:07:16 Device Bypass input voltage is no longer out of tolerance. 0x3736 03/12/2025 08:07:16 Device Static bypass switch is OK and working correctly. 0x37B8 03/12/2025 08:07:16 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 03/12/2025 08:07:16 Device The UPS inverter output is not in phase with the bypass input. 0x3722 03/12/2025 08:07:16 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 03/12/2025 08:07:16 Device Bypass input voltage is no longer out of tolerance. 0x3736 03/12/2025 08:07:15 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 03/11/2025 14:50:05 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/11/2025 14:49:56 Device Communication between Main Controller and display is fine. 0x370B 03/11/2025 14:49:31 Device Main Controller is unable to communicate with the display. 0x370C 03/11/2025 11:58:27 Device UPS time has been changed. 0x3790 03/10/2025 11:58:27 Device UPS time has been changed. 0x3790 03/09/2025 11:58:26 Device UPS time has been changed. 0x3790 03/08/2025 11:58:31 Device UPS time has been changed. 0x3790 03/07/2025 10:52:58 Device UPS time has been changed. 0x3790 03/07/2025 11:58:19 Device UPS time has been changed. 0x3790 03/07/2025 11:08:41 Device Charge voltage is set to float voltage level. 0x375C 03/07/2025 11:07:41 Device Charge voltage is set to boost charge level. 0x375E 03/07/2025 11:07:41 Device Charge voltage is set to float voltage level. 0x375C 03/07/2025 11:07:41 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 03/07/2025 11:07:41 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 03/07/2025 11:07:41 Device Battery self test is inactive. 0x37D9 03/07/2025 11:07:41 Device Battery capacity is above 75%. 0x37D5 03/07/2025 11:07:41 Device Battery self test has been completed. 0x37DC 03/07/2025 11:06:41 Device Charger is off. 0x3765 03/07/2025 11:06:41 Device On battery power in response to a test of the performance of the batteries. 0x3755 03/07/2025 11:06:41 Device Battery self test is running. 0x37DA 03/07/2025 11:06:41 Device User has activated battery self test function. 0x37DD 03/06/2025 11:58:19 Device UPS time has been changed. 0x3790 03/05/2025 11:58:21 Device UPS time has been changed. 0x3790 03/04/2025 11:58:19 Device UPS time has been changed. 0x3790 03/04/2025 00:07:01 Device Charge voltage is set to float voltage level. 0x375C 03/04/2025 00:06:01 Device Charge voltage is set to boost charge level. 0x375E 03/04/2025 00:06:01 Device Charge voltage is set to float voltage level. 0x375C 03/04/2025 00:06:01 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 03/04/2025 00:06:01 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 03/04/2025 00:06:01 Device Battery self test is inactive. 0x37D9 03/04/2025 00:06:01 Device Battery capacity is above 75%. 0x37D5 03/04/2025 00:06:01 Device Battery self test has been completed. 0x37DC 03/04/2025 00:05:01 Device Charger is off. 0x3765 03/04/2025 00:05:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 03/04/2025 00:05:01 Device Battery self test is running. 0x37DA 03/04/2025 00:05:00 Device A scheduled battery self-test has been started. 0x37D3 03/03/2025 11:58:19 Device UPS time has been changed. 0x3790 03/02/2025 11:58:19 Device UPS time has been changed. 0x3790 03/01/2025 11:58:19 Device UPS time has been changed. 0x3790 02/28/2025 16:11:12 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/28/2025 16:11:12 Device The user has requested a transfer to inverter. 0x37AE 02/28/2025 16:11:09 Device The output voltage is no longer out of tolerance. 0x3728 02/28/2025 16:11:09 Device Output frequency is no longer out of tolerance. 0x372A 02/28/2025 16:11:09 Device The UPS is synchronized to the parallel system. 0x3727 02/28/2025 16:11:09 Device Unit output breaker UOB is closed. 0x37C2 02/28/2025 16:10:19 Device Modular battery cabinet 1 is ok. 0x37EE 02/28/2025 16:10:19 Device Modular battery cabinet 1 breaker 2 is closed. 0x37CE 02/28/2025 16:10:04 Device Modular battery cabinet 1 breaker 1 is closed. 0x37CE 02/28/2025 16:09:34 Device Modular battery cabinet 2 is ok. 0x37EE 02/28/2025 16:09:34 Device Modular battery cabinet 2 breaker 2 is closed. 0x37CE 02/28/2025 16:09:03 Device Modular battery cabinet 2 breaker 1 is closed. 0x37CE 02/28/2025 16:08:40 Device The battery runtime is above configured minimum acceptable value. 0x37E5 02/28/2025 16:08:09 Device Modular battery cabinet 3 is ok. 0x37EE 02/28/2025 16:08:08 Device Modular battery cabinet 3 breaker 1 is closed. 0x37CE 02/28/2025 16:07:59 Device Static bypass switch is OK and working correctly. 0x37B8 02/28/2025 16:07:58 Device The UPS inverter output is in phase with the bypass input. 0x3721 02/28/2025 16:07:58 Device The UPS is synchronized to the bypass input. 0x3711 02/28/2025 16:07:54 Device Bypass input is no longer missing a phase. 0x373E 02/28/2025 16:07:54 Device Bypass input voltage is no longer out of tolerance. 0x3736 02/28/2025 16:07:53 Device Bypass input frequency is no longer out of tolerance. 0x373A 02/28/2025 16:07:53 Device Bypass static switch input breaker SSIB is closed. 0x37C8 02/28/2025 16:06:46 Device The battery runtime is below configured minimum acceptable value. 0x37E6 02/28/2025 16:06:30 Device Battery is working correctly. 0x37D0 02/28/2025 16:06:28 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 02/28/2025 16:06:25 Device The load is supplied from the inverters of the system. One or more UPS is in normal or battery operation. 0x3761 02/28/2025 16:06:23 Device Static bypass switch is inoperable. UPS is prevented from going into static bypass operation. 0x37BA 02/28/2025 16:06:23 Device Bypass input frequency is out of tolerance. 0x373B 02/28/2025 16:06:23 Device Output frequency is out of tolerance. 0x372B 02/28/2025 16:06:23 Device The UPS is charging the batteries. 0x37E7 02/28/2025 16:06:23 Device Charge voltage is set to float voltage level. 0x375C 02/28/2025 16:06:23 Device The output power is turned off. 0x3756 02/28/2025 16:06:23 Device Charger is off. 0x3765 02/28/2025 16:06:23 Device Self test is passed. 0x0105 02/28/2025 16:06:23 Device Surveillance OK. 0x3780 02/28/2025 16:06:11 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 02/28/2025 16:06:11 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 02/28/2025 16:06:11 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 02/28/2025 16:06:11 Device Modular battery cabinet 1 breaker 1 is open. 0x37CF 02/28/2025 16:06:11 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 02/28/2025 16:06:09 Device All UPS fans are OK. 0x3784 02/28/2025 16:06:03 Device UPS has one or more inoperable fans. Fan redundancy is lost. 0x3785 02/28/2025 16:06:01 Device The battery state is unknown. Either the battery is new or a battery runtime calibration test has been aborted. 0x37D6 02/28/2025 16:06:01 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/28/2025 16:06:01 Device The output voltage is out of tolerance. 0x3729 02/28/2025 16:06:01 Device Bypass input is missing a phase. 0x373F 02/28/2025 16:06:01 Device Battery is not working correctly. 0x37D1 02/28/2025 16:06:01 Device Surveillance detected fault. 0x3781 02/28/2025 16:06:01 Device Modular battery cabinet 3 is not working correctly. 0x37EF 02/28/2025 16:06:01 Device Modular battery cabinet 2 is not working correctly. 0x37EF 02/28/2025 16:06:01 Device Modular battery cabinet 1 is not working correctly. 0x37EF 02/28/2025 16:06:01 Device Not enough UPS units ready to turn on inverter cleared. 0x3778 02/28/2025 16:06:01 Device The system output power is turned off. 0x3760 02/28/2025 16:06:01 Device Unit output breaker UOB is open, and UPS cannot feed the load. 0x37C3 02/28/2025 16:06:01 Device Bypass static switch input breaker SSIB is open, making static bypass operation unavailable. 0x37C9 02/28/2025 16:06:01 Device The UPS inverter output is not in phase with the bypass input. 0x3722 02/28/2025 16:06:01 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 02/28/2025 16:06:01 Device Controller has booted and is ready to run. 0x3701 02/26/2025 11:59:22 Device UPS has one or more inoperable fans. Fan redundancy is lost. 0x3785 02/26/2025 11:59:21 Device Charger is off. 0x3765 02/26/2025 11:59:19 Device Charge voltage is set to float voltage level. 0x375C 02/26/2025 11:59:18 Device Surveillance detected fault. 0x3781 02/26/2025 11:59:14 Device Input is missing a phase. 0x373D 02/26/2025 11:59:14 Device Mains input frequency is out of tolerance. 0x3735 02/26/2025 11:59:13 Device Battery is not working correctly. 0x37D1 02/26/2025 11:59:13 Device Charger is off. 0x3765 02/26/2025 11:59:13 Device Mains input voltage is out of tolerance. 0x3731 02/26/2025 11:59:13 Device Unit input breaker UIB is open, and the UPS is prevented from running in normal operation. 0x37C1 02/26/2025 11:59:01 Device Modular battery cabinet 3 is not working correctly. 0x37EF 02/26/2025 11:59:01 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 02/26/2025 11:58:51 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 02/26/2025 11:58:47 Device Modular battery cabinet 2 is not working correctly. 0x37EF 02/26/2025 11:58:47 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 02/26/2025 11:58:38 Device Modular battery cabinet 1 breaker 1 is open. 0x37CF 02/26/2025 11:58:35 Device Modular battery cabinet 1 is not working correctly. 0x37EF 02/26/2025 11:58:35 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 02/26/2025 11:58:26 Device Bypass input frequency is out of tolerance. 0x373B 02/26/2025 11:58:26 Device Output frequency is out of tolerance. 0x372B 02/26/2025 11:58:26 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 02/26/2025 11:58:26 Device Bypass input is missing a phase. 0x373F 02/26/2025 11:58:26 Device The inverter is no longer off due to a request by the user. 0x37B5 02/26/2025 11:58:26 Device The output power is turned off. 0x3756 02/26/2025 11:58:26 Device Static bypass switch is inoperable. UPS is prevented from going into static bypass operation. 0x37BA 02/26/2025 11:58:26 Device The UPS inverter output is not in phase with the bypass input. 0x3722 02/26/2025 11:58:26 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 02/26/2025 11:58:26 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/26/2025 11:58:26 Device The output voltage is out of tolerance. 0x3729 02/26/2025 11:58:25 Device Bypass static switch input breaker SSIB is open, making static bypass operation unavailable. 0x37C9 02/26/2025 11:57:51 Device The output voltage is no longer out of tolerance. 0x3728 02/26/2025 11:57:51 Device The UPS is synchronized to the bypass input. 0x3711 02/26/2025 11:57:51 Device The UPS is in bypass in response to a critical event or an inverter off request. 0x3753 02/26/2025 11:57:51 Device Unit output breaker UOB is open, and UPS cannot feed the load. 0x37C3 02/26/2025 11:57:51 Device The output voltage is out of tolerance. 0x3729 02/26/2025 11:56:53 Device The UPS is synchronized to the parallel system. 0x3727 02/26/2025 11:56:52 Device The UPS is ready to enter static bypass but awaits permission from the system. UPS output is off. 0x3758 02/26/2025 11:56:52 Device The inverter is off due to a request by the user. 0x37B6 02/26/2025 11:56:52 Device The user has requested to turn off the inverter. 0x37AF 02/25/2025 13:36:09 Device UPS time has been changed. 0x3790 02/25/2025 00:07:01 Device Charge voltage is set to float voltage level. 0x375C 02/25/2025 00:06:11 Device The UPS is charging the batteries. 0x37E7 02/25/2025 00:06:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 02/25/2025 00:06:01 Device Charge voltage is set to boost charge level. 0x375E 02/25/2025 00:06:01 Device Charge voltage is set to float voltage level. 0x375C 02/25/2025 00:06:01 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/25/2025 00:06:01 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 02/25/2025 00:06:01 Device Battery self test is inactive. 0x37D9 02/25/2025 00:06:01 Device Battery capacity is above 75%. 0x37D5 02/25/2025 00:06:01 Device Battery self test has been completed. 0x37DC 02/25/2025 00:05:01 Device Charger is off. 0x3765 02/25/2025 00:05:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 02/25/2025 00:05:01 Device Battery self test is running. 0x37DA 02/25/2025 00:05:00 Device A scheduled battery self-test has been started. 0x37D3 02/24/2025 13:36:09 Device UPS time has been changed. 0x3790 02/23/2025 13:36:10 Device UPS time has been changed. 0x3790 02/22/2025 13:36:08 Device UPS time has been changed. 0x3790 02/21/2025 13:36:03 Device UPS time has been changed. 0x3790 02/20/2025 16:21:02 Device The UPS is synchronized to the bypass input. 0x3711 02/20/2025 14:28:38 Device The load is supplied from the inverters of the system. One or more UPS is in normal or battery operation. 0x3761 02/20/2025 14:28:38 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/20/2025 14:28:36 Device The system is in bypass in response to a critical event or an inverter off request. 0x3762 02/20/2025 14:28:36 Device The UPS is in bypass in response to a critical event or an inverter off request. 0x3753 02/20/2025 14:28:36 Device Maintenance bypass breaker MBB is open. 0x37C4 02/20/2025 14:28:27 Device The UPS load is supplied through Maintenance Bypass Breaker (MBB). 0x3754 02/20/2025 14:28:27 Device System isolation breaker SIB is closed. 0x37C6 02/20/2025 14:27:15 Device The UPS is synchronized to the parallel system. 0x3727 02/20/2025 14:27:15 Device Unit output breaker UOB is closed. 0x37C2 02/20/2025 14:27:07 Device The battery runtime is above configured minimum acceptable value. 0x37E5 02/20/2025 14:27:06 Device The output voltage is no longer out of tolerance. 0x3728 02/20/2025 14:27:06 Device Output frequency is no longer out of tolerance. 0x372A 02/20/2025 14:27:05 Device The UPS is in bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance. 0x3752 02/20/2025 14:27:05 Device The user has requested a transfer from inverter to bypass. 0x37AC 02/20/2025 14:26:59 Device Modular battery cabinet 3 is ok. 0x37EE 02/20/2025 14:26:59 Device Modular battery cabinet 3 breaker 1 is closed. 0x37CE 02/20/2025 14:26:51 Device Modular battery cabinet 2 is ok. 0x37EE 02/20/2025 14:26:51 Device Modular battery cabinet 2 breaker 1 is closed. 0x37CE 02/20/2025 14:26:49 Device Modular battery cabinet 2 breaker 2 is closed. 0x37CE 02/20/2025 14:26:42 Device Modular battery cabinet 1 is ok. 0x37EE 02/20/2025 14:26:42 Device Modular battery cabinet 1 breaker 1 is closed. 0x37CE 02/20/2025 14:26:35 Device Modular battery cabinet 1 breaker 2 is closed. 0x37CE 02/20/2025 14:26:30 Device Static bypass switch is OK and working correctly. 0x37B8 02/20/2025 14:26:27 Device The UPS inverter output is in phase with the bypass input. 0x3721 02/20/2025 14:26:27 Device The UPS is synchronized to the bypass input. 0x3711 02/20/2025 14:26:23 Device Bypass input is no longer missing a phase. 0x373E 02/20/2025 14:26:22 Device Bypass input voltage is no longer out of tolerance. 0x3736 02/20/2025 14:26:22 Device Bypass input frequency is no longer out of tolerance. 0x373A 02/20/2025 14:26:22 Device Bypass static switch input breaker SSIB is closed. 0x37C8 02/20/2025 14:25:44 Device UPS time has been changed. 0x3790 02/20/2025 14:25:50 Device The system load is supplied through Maintenance Bypass Breaker (MBB). 0x3764 02/20/2025 13:54:06 Device Communication to parallel UPS 1 is obtained. 0x377C 02/20/2025 13:54:05 Device PBUS cable 2 is fine. 0x3772 02/20/2025 13:54:05 Device PBUS cable 1 is fine. 0x3770 02/20/2025 13:49:59 Device Main Controller is unable to communicate with parallel UPS 1. The UPS might have been powered down or communication cables may be damaged. 0x377D 02/20/2025 13:49:58 Device PBUS cable 2 may be damaged. 0x3773 02/20/2025 13:49:58 Device PBUS cable 1 may be damaged. 0x3771 02/20/2025 13:35:31 Device The battery runtime is below configured minimum acceptable value. 0x37E6 02/20/2025 13:35:15 Device Battery is working correctly. 0x37D0 02/20/2025 13:35:14 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 02/20/2025 13:35:08 Device Static bypass switch is inoperable. UPS is prevented from going into static bypass operation. 0x37BA 02/20/2025 13:35:08 Device Bypass input frequency is out of tolerance. 0x373B 02/20/2025 13:35:08 Device Output frequency is out of tolerance. 0x372B 02/20/2025 13:35:08 Device The UPS is charging the batteries. 0x37E7 02/20/2025 13:35:08 Device Charge voltage is set to float voltage level. 0x375C 02/20/2025 13:35:08 Device The output power is turned off. 0x3756 02/20/2025 13:35:08 Device Charger is off. 0x3765 02/20/2025 13:35:08 Device Self test is passed. 0x0105 02/20/2025 13:35:08 Device Surveillance OK. 0x3780 02/20/2025 13:34:56 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 02/20/2025 13:34:56 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 02/20/2025 13:34:56 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 02/20/2025 13:34:56 Device Modular battery cabinet 1 breaker 1 is open. 0x37CF 02/20/2025 13:34:55 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 02/20/2025 13:34:54 Device All UPS fans are OK. 0x3784 02/20/2025 13:34:48 Device UPS has one or more inoperable fans. Fan redundancy is lost. 0x3785 02/20/2025 13:34:46 Device The battery state is unknown. Either the battery is new or a battery runtime calibration test has been aborted. 0x37D6 02/20/2025 13:34:46 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/20/2025 13:34:46 Device The output voltage is out of tolerance. 0x3729 02/20/2025 13:34:46 Device Bypass input is missing a phase. 0x373F 02/20/2025 13:34:46 Device Battery is not working correctly. 0x37D1 02/20/2025 13:34:46 Device Surveillance detected fault. 0x3781 02/20/2025 13:34:46 Device Modular battery cabinet 3 is not working correctly. 0x37EF 02/20/2025 13:34:46 Device Modular battery cabinet 2 is not working correctly. 0x37EF 02/20/2025 13:34:46 Device Modular battery cabinet 1 is not working correctly. 0x37EF 02/20/2025 13:34:46 Device Not enough UPS units ready to turn on inverter cleared. 0x3778 02/20/2025 13:34:46 Device The system load is supplied through Maintenance Bypass Breaker (MBB). 0x3764 02/20/2025 13:34:46 Device Unit output breaker UOB is open, and UPS cannot feed the load. 0x37C3 02/20/2025 13:34:46 Device Bypass static switch input breaker SSIB is open, making static bypass operation unavailable. 0x37C9 02/20/2025 13:34:46 Device Maintenance bypass breaker MBB is closed, feeding the load with unprotected power from bypass. 0x37C5 02/20/2025 13:34:46 Device The UPS inverter output is not in phase with the bypass input. 0x3722 02/20/2025 13:34:46 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 02/20/2025 13:34:46 Device The system output power is turned off. 0x3760 02/20/2025 13:34:46 Device System isolation breaker SIB is open, and system cannot feed the load. 0x37C7 02/20/2025 13:34:46 Device Controller has booted and is ready to run. 0x3701 02/20/2025 13:34:26 Device Mains input voltage is out of tolerance. 0x3731 02/20/2025 13:34:25 Device Battery is not working correctly. 0x37D1 02/20/2025 13:34:24 Device Modular battery cabinet 3 is not working correctly. 0x37EF 02/20/2025 13:34:24 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 02/20/2025 13:34:12 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 02/20/2025 13:34:09 Device Modular battery cabinet 2 is not working correctly. 0x37EF 02/20/2025 13:34:09 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 02/20/2025 13:34:00 Device Modular battery cabinet 1 breaker 1 is open. 0x37CF 02/20/2025 13:33:58 Device Modular battery cabinet 1 is not working correctly. 0x37EF 02/20/2025 13:33:58 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 02/20/2025 13:33:46 Device Bypass input frequency is out of tolerance. 0x373B 02/20/2025 13:33:46 Device Output frequency is out of tolerance. 0x372B 02/20/2025 13:33:45 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 02/20/2025 13:33:45 Device Bypass input is missing a phase. 0x373F 02/20/2025 13:33:45 Device Static bypass switch is inoperable. UPS is prevented from going into static bypass operation. 0x37BA 02/20/2025 13:33:45 Device The output power is turned off. 0x3756 02/20/2025 13:33:45 Device The UPS inverter output is not in phase with the bypass input. 0x3722 02/20/2025 13:33:45 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 02/20/2025 13:33:45 Device The output voltage is out of tolerance. 0x3729 02/20/2025 13:33:45 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/20/2025 13:33:45 Device Bypass static switch input breaker SSIB is open, making static bypass operation unavailable. 0x37C9 02/20/2025 13:33:36 Device Unit output breaker UOB is open, and UPS cannot feed the load. 0x37C3 02/20/2025 13:33:07 Device The UPS is in bypass in response to a critical event or an inverter off request. 0x3753 02/20/2025 13:33:07 Device System isolation breaker SIB is open, and system cannot feed the load. 0x37C7 02/20/2025 13:32:51 Device The UPS load is supplied through Maintenance Bypass Breaker (MBB). 0x3754 02/20/2025 13:32:51 Device The system load is supplied through Maintenance Bypass Breaker (MBB). 0x3764 02/20/2025 13:32:51 Device Maintenance bypass breaker MBB is closed, feeding the load with unprotected power from bypass. 0x37C5 02/20/2025 13:29:10 Device Charger is off. 0x3765 02/20/2025 13:29:10 Device Surveillance detected fault. 0x3781 02/20/2025 13:29:10 Device Not enough UPS units ready to turn on inverter cleared. 0x3778 02/20/2025 13:29:10 Device Charge voltage is set to float voltage level. 0x375C 02/20/2025 13:29:10 Device One or more parallel UPS units have been requested to turn on inverter, but not enough UPS units are ready for system to enter inverter on operation. 0x3779 02/20/2025 13:29:10 Device Charger is off. 0x3765 02/20/2025 13:29:10 Device Charge voltage is set to float voltage level. 0x375C 02/20/2025 13:29:10 Device Surveillance OK. 0x3780 02/20/2025 13:29:08 Device Charger is off. 0x3765 02/20/2025 13:29:08 Device Surveillance detected fault. 0x3781 02/20/2025 13:29:08 Device Not enough UPS units ready to turn on inverter cleared. 0x3778 02/20/2025 13:29:08 Device Charge voltage is set to float voltage level. 0x375C 02/20/2025 13:29:08 Device One or more parallel UPS units have been requested to turn on inverter, but not enough UPS units are ready for system to enter inverter on operation. 0x3779 02/20/2025 13:29:08 Device Charger is off. 0x3765 02/20/2025 13:29:08 Device Charge voltage is set to float voltage level. 0x375C 02/20/2025 13:29:08 Device Surveillance OK. 0x3780 02/20/2025 13:29:06 Device The UPS is in bypass in response to a critical event or an inverter off request. 0x3753 02/20/2025 13:29:06 Device The system is in bypass in response to a critical event or an inverter off request. 0x3762 02/20/2025 13:29:06 Device Charger is off. 0x3765 02/20/2025 13:29:06 Device Surveillance detected fault. 0x3781 02/20/2025 13:26:28 Device Communication to parallel UPS 1 is obtained. 0x377C 02/20/2025 13:26:27 Device PBUS cable 2 is fine. 0x3772 02/20/2025 13:26:27 Device PBUS cable 1 is fine. 0x3770 02/20/2025 11:35:05 Device UPS time has been changed. 0x3790 02/19/2025 11:35:05 Device UPS time has been changed. 0x3790 02/18/2025 11:35:05 Device UPS time has been changed. 0x3790 02/17/2025 13:27:03 Device The UPS inverter output is in phase with the bypass input. 0x3721 02/17/2025 13:27:03 Device The UPS is synchronized to the bypass input. 0x3711 02/17/2025 13:27:01 Device Bypass input voltage is no longer out of tolerance. 0x3736 02/17/2025 13:27:01 Device The UPS inverter output is not in phase with the bypass input. 0x3722 02/17/2025 13:27:01 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 02/17/2025 13:27:01 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/17/2025 13:00:26 Device Main Controller is unable to communicate with parallel UPS 1. The UPS might have been powered down or communication cables may be damaged. 0x377D 02/17/2025 13:00:25 Device PBUS cable 2 may be damaged. 0x3773 02/17/2025 13:00:25 Device PBUS cable 1 may be damaged. 0x3771 02/17/2025 11:34:11 Device Charge voltage is set to float voltage level. 0x375C 02/17/2025 11:33:41 Device The UPS is synchronized to the bypass input. 0x3711 02/17/2025 11:33:41 Device All parallel UPS units have the same operation mode. 0x377A 02/17/2025 11:33:31 Device One or more parallel UPS units are operating in battery operation, while others are operating in normal operation. 0x377B 02/17/2025 11:33:21 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/17/2025 11:33:12 Device Input is no longer missing a phase. 0x373C 02/17/2025 11:33:11 Device Charge voltage is set to boost charge level. 0x375E 02/17/2025 11:33:11 Device Charge voltage is set to float voltage level. 0x375C 02/17/2025 11:33:11 Device Mains input voltage is no longer out of tolerance. 0x3730 02/17/2025 11:33:11 Device Mains input frequency is no longer out of tolerance. 0x3734 02/17/2025 11:33:11 Device All parallel UPS units have the same operation mode. 0x377A 02/17/2025 11:33:11 Device The UPS is ready to enter battery operation but awaits permission from the system. UPS output is off. 0x3759 02/17/2025 11:33:01 Device One or more parallel UPS units are operating in battery operation, while others are operating in normal operation. 0x377B 02/17/2025 11:32:57 Device Mains input frequency is out of tolerance. 0x3735 02/17/2025 11:32:56 Device Input is missing a phase. 0x373D 02/17/2025 11:32:56 Device Charger is off. 0x3765 02/17/2025 11:32:56 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 02/17/2025 11:32:56 Device Mains input voltage is out of tolerance. 0x3731 02/17/2025 06:35:35 Device UPS time has been changed. 0x3790 02/16/2025 06:35:36 Device UPS time has been changed. 0x3790 02/15/2025 06:35:36 Device UPS time has been changed. 0x3790 02/14/2025 06:35:35 Device UPS time has been changed. 0x3790 02/13/2025 06:35:35 Device UPS time has been changed. 0x3790 02/12/2025 06:35:36 Device UPS time has been changed. 0x3790 02/11/2025 06:35:35 Device UPS time has been changed. 0x3790 02/10/2025 06:35:36 Device UPS time has been changed. 0x3790 02/09/2025 06:35:36 Device UPS time has been changed. 0x3790 02/08/2025 06:35:35 Device UPS time has been changed. 0x3790 02/07/2025 16:35:08 Device Bypass input voltage is no longer out of tolerance. 0x3736 02/07/2025 16:35:08 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/07/2025 13:45:59 Device Bypass input voltage is no longer out of tolerance. 0x3736 02/07/2025 13:45:59 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/07/2025 06:35:35 Device UPS time has been changed. 0x3790 02/06/2025 06:35:37 Device UPS time has been changed. 0x3790 02/05/2025 06:35:35 Device UPS time has been changed. 0x3790 02/04/2025 06:35:36 Device UPS time has been changed. 0x3790 02/03/2025 06:35:35 Device UPS time has been changed. 0x3790 02/02/2025 06:35:36 Device UPS time has been changed. 0x3790 02/01/2025 06:35:36 Device UPS time has been changed. 0x3790 01/31/2025 06:35:35 Device UPS time has been changed. 0x3790 01/30/2025 06:35:35 Device UPS time has been changed. 0x3790 01/29/2025 06:35:36 Device UPS time has been changed. 0x3790 01/28/2025 06:35:36 Device UPS time has been changed. 0x3790 01/27/2025 19:21:02 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 19:20:59 Device The UPS inverter output is in phase with the bypass input. 0x3721 01/27/2025 19:20:55 Device Bypass input is no longer missing a phase. 0x373E 01/27/2025 19:20:55 Device Bypass input voltage is no longer out of tolerance. 0x3736 01/27/2025 19:20:54 Device Bypass input frequency is no longer out of tolerance. 0x373A 01/27/2025 19:20:54 Device Static bypass switch is OK and working correctly. 0x37B8 01/27/2025 19:20:50 Device Bypass input frequency is out of tolerance. 0x373B 01/27/2025 19:20:49 Device Bypass input is missing a phase. 0x373F 01/27/2025 19:20:49 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 01/27/2025 19:20:49 Device The UPS inverter output is not in phase with the bypass input. 0x3722 01/27/2025 19:20:49 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 01/27/2025 19:20:12 Device The UPS is charging the batteries. 0x37E7 01/27/2025 19:20:03 Device Input is no longer missing a phase. 0x373C 01/27/2025 19:20:02 Device Charge voltage is set to boost charge level. 0x375E 01/27/2025 19:20:02 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 19:20:02 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 01/27/2025 19:20:02 Device Mains input voltage is no longer out of tolerance. 0x3730 01/27/2025 19:20:02 Device Mains input frequency is no longer out of tolerance. 0x3734 01/27/2025 19:19:57 Device Mains input frequency is out of tolerance. 0x3735 01/27/2025 19:19:57 Device Input is missing a phase. 0x373D 01/27/2025 19:19:57 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 01/27/2025 19:19:56 Device Charger is off. 0x3765 01/27/2025 19:19:56 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 01/27/2025 19:19:56 Device Mains input voltage is out of tolerance. 0x3731 01/27/2025 18:57:52 Device The UPS inverter output is in phase with the bypass input. 0x3721 01/27/2025 18:57:51 Device The UPS inverter output is not in phase with the bypass input. 0x3722 01/27/2025 18:56:52 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 18:56:24 Device The UPS inverter output is in phase with the bypass input. 0x3721 01/27/2025 18:56:22 Device Static bypass switch is OK and working correctly. 0x37B8 01/27/2025 18:56:22 Device Bypass input is no longer missing a phase. 0x373E 01/27/2025 18:56:21 Device Bypass input voltage is no longer out of tolerance. 0x3736 01/27/2025 18:56:21 Device Bypass input frequency is no longer out of tolerance. 0x373A 01/27/2025 18:56:02 Device The UPS is charging the batteries. 0x37E7 01/27/2025 18:55:53 Device Input is no longer missing a phase. 0x373C 01/27/2025 18:55:52 Device Charge voltage is set to boost charge level. 0x375E 01/27/2025 18:55:52 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 18:55:52 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 01/27/2025 18:55:52 Device Mains input voltage is no longer out of tolerance. 0x3730 01/27/2025 18:55:52 Device Mains input frequency is no longer out of tolerance. 0x3734 01/27/2025 18:55:34 Device Bypass input frequency is out of tolerance. 0x373B 01/27/2025 18:55:34 Device Mains input frequency is out of tolerance. 0x3735 01/27/2025 18:55:34 Device Input is missing a phase. 0x373D 01/27/2025 18:55:34 Device Bypass input is missing a phase. 0x373F 01/27/2025 18:55:33 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 01/27/2025 18:55:33 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 01/27/2025 18:55:33 Device The UPS inverter output is not in phase with the bypass input. 0x3722 01/27/2025 18:55:33 Device Charger is off. 0x3765 01/27/2025 18:55:33 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 01/27/2025 18:55:33 Device Mains input voltage is out of tolerance. 0x3731 01/27/2025 18:55:33 Device Static bypass switch is OK and working correctly. 0x37B8 01/27/2025 18:55:33 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 01/27/2025 18:55:33 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 01/27/2025 06:35:35 Device UPS time has been changed. 0x3790 01/26/2025 06:35:35 Device UPS time has been changed. 0x3790 01/25/2025 06:35:36 Device UPS time has been changed. 0x3790 01/24/2025 14:53:09 Device Bypass input voltage is no longer out of tolerance. 0x3736 01/24/2025 14:53:09 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 01/24/2025 06:35:36 Device UPS time has been changed. 0x3790 01/23/2025 06:35:35 Device UPS time has been changed. 0x3790 01/22/2025 06:35:35 Device UPS time has been changed. 0x3790 01/21/2025 06:35:36 Device UPS time has been changed. 0x3790 01/21/2025 01:06:01 Device Charge voltage is set to float voltage level. 0x375C 01/21/2025 01:05:11 Device The UPS is charging the batteries. 0x37E7 01/21/2025 01:05:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 01/21/2025 01:05:01 Device Charge voltage is set to boost charge level. 0x375E 01/21/2025 01:05:01 Device Charge voltage is set to float voltage level. 0x375C 01/21/2025 01:05:01 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 01/21/2025 01:05:01 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 01/21/2025 01:05:01 Device Battery self test is inactive. 0x37D9 01/21/2025 01:05:01 Device Battery capacity is above 75%. 0x37D5 01/21/2025 01:05:01 Device Battery self test has been completed. 0x37DC 01/21/2025 00:05:01 Device Charger is off. 0x3765 01/21/2025 00:05:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 01/21/2025 00:05:01 Device Battery self test is running. 0x37DA 01/20/2025 06:35:35 Device UPS time has been changed. 0x3790 01/19/2025 06:35:36 Device UPS time has been changed. 0x3790 01/18/2025 06:35:35 Device UPS time has been changed. 0x3790 01/17/2025 06:35:35 Device UPS time has been changed. 0x3790 01/16/2025 06:35:35 Device UPS time has been changed. 0x3790 01/15/2025 06:35:37 Device UPS time has been changed. 0x3790 01/14/2025 06:35:35 Device UPS time has been changed. 0x3790 01/13/2025 06:35:35 Device UPS time has been changed. 0x3790 01/12/2025 06:35:35 Device UPS time has been changed. 0x3790 01/11/2025 06:35:36 Device UPS time has been changed. 0x3790 01/10/2025 06:35:36 Device UPS time has been changed. 0x3790 01/09/2025 06:35:35 Device UPS time has been changed. 0x3790 01/08/2025 06:35:36 Device UPS time has been changed. 0x3790 01/07/2025 06:35:35 Device UPS time has been changed. 0x3790 01/06/2025 06:35:36 Device UPS time has been changed. 0x3790 01/05/2025 06:35:36 Device UPS time has been changed. 0x3790 01/04/2025 06:35:35 Device UPS time has been changed. 0x3790 01/03/2025 06:35:35 Device UPS time has been changed. 0x3790 01/02/2025 06:35:36 Device UPS time has been changed. 0x3790 01/01/2025 06:35:36 Device UPS time has been changed. 0x3790 12/31/2024 06:35:35 Device UPS time has been changed. 0x3790 12/30/2024 06:35:36 Device UPS time has been changed. 0x3790 12/29/2024 06:35:35 Device UPS time has been changed. 0x3790 12/28/2024 06:35:36 Device UPS time has been changed. 0x3790 12/27/2024 06:35:36 Device UPS time has been changed. 0x3790 12/26/2024 06:35:35 Device UPS time has been changed. 0x3790 12/25/2024 06:35:35 Device UPS time has been changed. 0x3790 12/24/2024 06:35:35 Device UPS time has been changed. 0x3790 12/23/2024 06:35:37 Device UPS time has been changed. 0x3790 12/22/2024 06:35:35 Device UPS time has been changed. 0x3790 12/21/2024 06:35:35 Device UPS time has been changed. 0x3790 12/20/2024 06:35:35 Device UPS time has been changed. 0x3790 12/19/2024 06:35:36 Device UPS time has been changed. 0x3790 12/18/2024 08:25:27 Device The UPS is charging the batteries. 0x37E7 12/18/2024 08:25:17 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/18/2024 08:25:17 Device Charge voltage is set to float voltage level. 0x375C 12/18/2024 08:25:17 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/18/2024 08:25:17 Device Surveillance OK. 0x3780 12/18/2024 08:25:16 Device The UPS is ready to enter static bypass but awaits permission from the system. UPS output is off. 0x3758 12/18/2024 08:25:16 Device Charger is off. 0x3765 12/18/2024 08:25:16 Device Surveillance detected fault. 0x3781 12/18/2024 06:35:36 Device UPS time has been changed. 0x3790 12/17/2024 06:35:35 Device UPS time has been changed. 0x3790 12/17/2024 02:23:48 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 02:23:46 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/17/2024 02:23:43 Device Bypass input is no longer missing a phase. 0x373E 12/17/2024 02:23:42 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/17/2024 02:23:42 Device Bypass input frequency is no longer out of tolerance. 0x373A 12/17/2024 02:23:42 Device Static bypass switch is OK and working correctly. 0x37B8 12/17/2024 02:23:38 Device Bypass input frequency is out of tolerance. 0x373B 12/17/2024 02:23:37 Device Bypass input is missing a phase. 0x373F 12/17/2024 02:23:37 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 12/17/2024 02:23:37 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/17/2024 02:23:37 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/17/2024 02:22:58 Device The UPS is charging the batteries. 0x37E7 12/17/2024 02:22:49 Device Input is no longer missing a phase. 0x373C 12/17/2024 02:22:48 Device Charge voltage is set to boost charge level. 0x375E 12/17/2024 02:22:48 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 02:22:48 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/17/2024 02:22:48 Device Mains input voltage is no longer out of tolerance. 0x3730 12/17/2024 02:22:48 Device Mains input frequency is no longer out of tolerance. 0x3734 12/17/2024 02:22:44 Device Mains input frequency is out of tolerance. 0x3735 12/17/2024 02:22:44 Device Input is missing a phase. 0x373D 12/17/2024 02:22:43 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/17/2024 02:22:43 Device Charger is off. 0x3765 12/17/2024 02:22:43 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/17/2024 02:22:43 Device Mains input voltage is out of tolerance. 0x3731 12/17/2024 02:09:33 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/17/2024 02:09:30 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/17/2024 02:08:25 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/17/2024 02:08:23 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/17/2024 01:02:25 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 01:01:55 Device Static bypass switch is OK and working correctly. 0x37B8 12/17/2024 01:01:55 Device Bypass input is no longer missing a phase. 0x373E 12/17/2024 01:01:55 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/17/2024 01:01:54 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/17/2024 01:01:54 Device Bypass input frequency is no longer out of tolerance. 0x373A 12/17/2024 01:01:35 Device The UPS is charging the batteries. 0x37E7 12/17/2024 01:01:26 Device Input is no longer missing a phase. 0x373C 12/17/2024 01:01:25 Device Charge voltage is set to boost charge level. 0x375E 12/17/2024 01:01:25 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 01:01:25 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/17/2024 01:01:25 Device Mains input voltage is no longer out of tolerance. 0x3730 12/17/2024 01:01:25 Device Mains input frequency is no longer out of tolerance. 0x3734 12/17/2024 01:01:07 Device Bypass input frequency is out of tolerance. 0x373B 12/17/2024 01:01:07 Device Mains input frequency is out of tolerance. 0x3735 12/17/2024 01:01:07 Device Input is missing a phase. 0x373D 12/17/2024 01:01:07 Device Bypass input is missing a phase. 0x373F 12/17/2024 01:01:07 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 12/17/2024 01:01:06 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/17/2024 01:01:06 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/17/2024 01:01:06 Device Charger is off. 0x3765 12/17/2024 01:01:06 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/17/2024 01:01:06 Device Mains input voltage is out of tolerance. 0x3731 12/17/2024 01:01:06 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/16/2024 06:35:35 Device UPS time has been changed. 0x3790 12/15/2024 06:35:35 Device UPS time has been changed. 0x3790 12/14/2024 06:35:36 Device UPS time has been changed. 0x3790 12/13/2024 08:18:07 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 08:18:04 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/13/2024 08:18:01 Device Bypass input is no longer missing a phase. 0x373E 12/13/2024 08:18:01 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/13/2024 08:18:00 Device Bypass input frequency is no longer out of tolerance. 0x373A 12/13/2024 08:18:00 Device Static bypass switch is OK and working correctly. 0x37B8 12/13/2024 08:17:56 Device Bypass input frequency is out of tolerance. 0x373B 12/13/2024 08:17:55 Device Bypass input is missing a phase. 0x373F 12/13/2024 08:17:55 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 12/13/2024 08:17:55 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/13/2024 08:17:55 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/13/2024 08:17:17 Device The UPS is charging the batteries. 0x37E7 12/13/2024 08:17:08 Device Input is no longer missing a phase. 0x373C 12/13/2024 08:17:08 Device Charge voltage is set to boost charge level. 0x375E 12/13/2024 08:17:08 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 08:17:08 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/13/2024 08:17:08 Device Mains input voltage is no longer out of tolerance. 0x3730 12/13/2024 08:17:07 Device Mains input frequency is no longer out of tolerance. 0x3734 12/13/2024 08:17:03 Device Mains input frequency is out of tolerance. 0x3735 12/13/2024 08:17:03 Device Input is missing a phase. 0x373D 12/13/2024 08:17:03 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/13/2024 08:17:02 Device Charger is off. 0x3765 12/13/2024 08:17:02 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/13/2024 08:17:02 Device Mains input voltage is out of tolerance. 0x3731 12/13/2024 08:16:56 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 08:16:29 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/13/2024 08:16:27 Device Static bypass switch is OK and working correctly. 0x37B8 12/13/2024 08:16:27 Device Bypass input is no longer missing a phase. 0x373E 12/13/2024 08:16:26 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/13/2024 08:16:26 Device Bypass input frequency is no longer out of tolerance. 0x373A 12/13/2024 08:16:06 Device The UPS is charging the batteries. 0x37E7 12/13/2024 08:15:57 Device Input is no longer missing a phase. 0x373C 12/13/2024 08:15:56 Device Charge voltage is set to boost charge level. 0x375E 12/13/2024 08:15:56 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 08:15:56 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/13/2024 08:15:56 Device Mains input voltage is no longer out of tolerance. 0x3730 12/13/2024 08:15:56 Device Mains input frequency is no longer out of tolerance. 0x3734 12/13/2024 08:15:56 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/13/2024 08:15:39 Device Bypass input frequency is out of tolerance. 0x373B 12/13/2024 08:15:39 Device Mains input frequency is out of tolerance. 0x3735 12/13/2024 08:15:39 Device Input is missing a phase. 0x373D 12/13/2024 08:15:38 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 12/13/2024 08:15:38 Device Charger is off. 0x3765 12/13/2024 08:15:38 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/13/2024 08:15:38 Device Mains input voltage is out of tolerance. 0x3731 12/13/2024 08:15:38 Device Bypass input is missing a phase. 0x373F 12/13/2024 08:15:38 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/13/2024 08:15:38 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/13/2024 06:35:35 Device UPS time has been changed. 0x3790 12/12/2024 06:35:36 Device UPS time has been changed. 0x3790 12/12/2024 05:34:02 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 05:33:59 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 05:33:56 Device Bypass input is no longer missing a phase. 0x373E 12/12/2024 05:33:55 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/12/2024 05:33:55 Device Bypass input frequency is no longer out of tolerance. 0x373A 12/12/2024 05:33:55 Device Static bypass switch is OK and working correctly. 0x37B8 12/12/2024 05:33:50 Device Bypass input frequency is out of tolerance. 0x373B 12/12/2024 05:33:50 Device Bypass input is missing a phase. 0x373F 12/12/2024 05:33:50 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 12/12/2024 05:33:50 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 05:33:50 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/12/2024 05:33:12 Device The UPS is charging the batteries. 0x37E7 12/12/2024 05:33:03 Device Input is no longer missing a phase. 0x373C 12/12/2024 05:33:03 Device Charge voltage is set to boost charge level. 0x375E 12/12/2024 05:33:03 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 05:33:03 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/12/2024 05:33:03 Device Mains input voltage is no longer out of tolerance. 0x3730 12/12/2024 05:33:02 Device Mains input frequency is no longer out of tolerance. 0x3734 12/12/2024 05:32:58 Device Mains input frequency is out of tolerance. 0x3735 12/12/2024 05:32:58 Device Input is missing a phase. 0x373D 12/12/2024 05:32:58 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/12/2024 05:32:57 Device Charger is off. 0x3765 12/12/2024 05:32:57 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/12/2024 05:32:57 Device Mains input voltage is out of tolerance. 0x3731 12/12/2024 04:30:39 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 04:30:38 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 04:21:17 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 04:20:49 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 04:20:48 Device Static bypass switch is OK and working correctly. 0x37B8 12/12/2024 04:20:48 Device Bypass input is no longer missing a phase. 0x373E 12/12/2024 04:20:47 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/12/2024 04:20:47 Device Bypass input frequency is no longer out of tolerance. 0x373A 12/12/2024 04:20:27 Device The UPS is charging the batteries. 0x37E7 12/12/2024 04:20:18 Device Input is no longer missing a phase. 0x373C 12/12/2024 04:20:18 Device Charge voltage is set to boost charge level. 0x375E 12/12/2024 04:20:18 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 04:20:18 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/12/2024 04:20:18 Device Mains input voltage is no longer out of tolerance. 0x3730 12/12/2024 04:20:17 Device Mains input frequency is no longer out of tolerance. 0x3734 12/12/2024 04:20:00 Device Bypass input frequency is out of tolerance. 0x373B 12/12/2024 04:20:00 Device Mains input frequency is out of tolerance. 0x3735 12/12/2024 04:20:00 Device Input is missing a phase. 0x373D 12/12/2024 04:20:00 Device Bypass input is missing a phase. 0x373F 12/12/2024 04:19:59 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 12/12/2024 04:19:59 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/12/2024 04:19:59 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 04:19:59 Device Charger is off. 0x3765 12/12/2024 04:19:59 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/12/2024 04:19:59 Device Mains input voltage is out of tolerance. 0x3731 12/12/2024 04:19:59 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/11/2024 06:35:35 Device UPS time has been changed. 0x3790 12/10/2024 06:35:35 Device UPS time has been changed. 0x3790 12/09/2024 06:35:36 Device UPS time has been changed. 0x3790 12/08/2024 06:35:36 Device UPS time has been changed. 0x3790 12/07/2024 06:35:35 Device UPS time has been changed. 0x3790 12/06/2024 12:19:21 Device Bypass input voltage is no longer out of tolerance. 0x3736 12/06/2024 12:19:21 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 12/06/2024 08:11:37 Device The UPS is charging the batteries. 0x37E7 12/06/2024 08:11:27 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/06/2024 08:11:27 Device Charge voltage is set to float voltage level. 0x375C 12/06/2024 08:11:27 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/06/2024 08:11:27 Device Surveillance OK. 0x3780 12/06/2024 08:11:26 Device The UPS is ready to enter static bypass but awaits permission from the system. UPS output is off. 0x3758 12/06/2024 08:11:26 Device Charger is off. 0x3765 12/06/2024 08:11:26 Device Surveillance detected fault. 0x3781 12/06/2024 06:35:35 Device UPS time has been changed. 0x3790 12/05/2024 06:35:35 Device UPS time has been changed. 0x3790 12/04/2024 06:35:36 Device UPS time has been changed. 0x3790 12/03/2024 06:35:35 Device UPS time has been changed. 0x3790 12/02/2024 06:35:36 Device UPS time has been changed. 0x3790 12/01/2024 06:35:35 Device UPS time has been changed. 0x3790 11/30/2024 14:15:07 Device Charge voltage is set to float voltage level. 0x375C 11/30/2024 14:14:17 Device The UPS is charging the batteries. 0x37E7 11/30/2024 14:14:08 Device Input is no longer missing a phase. 0x373C 11/30/2024 14:14:07 Device Charge voltage is set to boost charge level. 0x375E 11/30/2024 14:14:07 Device Charge voltage is set to float voltage level. 0x375C 11/30/2024 14:14:07 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 11/30/2024 14:14:07 Device Mains input voltage is no longer out of tolerance. 0x3730 11/30/2024 14:14:07 Device Mains input frequency is no longer out of tolerance. 0x3734 11/30/2024 14:14:00 Device Mains input frequency is out of tolerance. 0x3735 11/30/2024 14:13:59 Device Input is missing a phase. 0x373D 11/30/2024 14:13:59 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/30/2024 14:13:59 Device Charger is off. 0x3765 11/30/2024 14:13:59 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 11/30/2024 14:13:59 Device Mains input voltage is out of tolerance. 0x3731 11/30/2024 06:35:36 Device UPS time has been changed. 0x3790 11/29/2024 17:06:09 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 11/29/2024 17:06:00 Device Communication between Main Controller and display is fine. 0x370B 11/29/2024 17:05:35 Device Main Controller is unable to communicate with the display. 0x370C 11/29/2024 16:51:16 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 11/29/2024 16:51:07 Device Communication between Main Controller and display is fine. 0x370B 11/29/2024 16:50:41 Device Main Controller is unable to communicate with the display. 0x370C 11/29/2024 06:35:35 Device UPS time has been changed. 0x3790 11/28/2024 06:35:35 Device UPS time has been changed. 0x3790 11/27/2024 06:35:36 Device UPS time has been changed. 0x3790 11/26/2024 06:35:35 Device UPS time has been changed. 0x3790 11/26/2024 01:06:01 Device Charge voltage is set to float voltage level. 0x375C 11/26/2024 01:05:11 Device The UPS is charging the batteries. 0x37E7 11/26/2024 01:05:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/26/2024 01:05:01 Device Charge voltage is set to boost charge level. 0x375E 11/26/2024 01:05:01 Device The UPS is charging the batteries. 0x37E7 11/26/2024 01:05:01 Device Charge voltage is set to float voltage level. 0x375C 11/26/2024 01:05:01 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 11/26/2024 01:05:01 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 11/26/2024 01:05:01 Device Battery self test is inactive. 0x37D9 11/26/2024 01:05:01 Device Battery capacity is above 75%. 0x37D5 11/26/2024 01:05:01 Device Battery self test has been completed. 0x37DC 11/26/2024 00:05:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/26/2024 00:05:01 Device Charger is off. 0x3765 11/26/2024 00:05:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 11/26/2024 00:05:01 Device Battery self test is running. 0x37DA 11/25/2024 06:35:36 Device UPS time has been changed. 0x3790 11/24/2024 08:05:45 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 08:05:42 Device The UPS inverter output is in phase with the bypass input. 0x3721 11/24/2024 08:05:38 Device Bypass input is no longer missing a phase. 0x373E 11/24/2024 08:05:38 Device Bypass input voltage is no longer out of tolerance. 0x3736 11/24/2024 08:05:37 Device Bypass input frequency is no longer out of tolerance. 0x373A 11/24/2024 08:05:37 Device Static bypass switch is OK and working correctly. 0x37B8 11/24/2024 08:05:33 Device Bypass input frequency is out of tolerance. 0x373B 11/24/2024 08:05:32 Device Bypass input is missing a phase. 0x373F 11/24/2024 08:05:32 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 11/24/2024 08:05:32 Device The UPS inverter output is not in phase with the bypass input. 0x3722 11/24/2024 08:05:32 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 11/24/2024 08:04:55 Device The UPS is charging the batteries. 0x37E7 11/24/2024 08:04:45 Device Input is no longer missing a phase. 0x373C 11/24/2024 08:04:45 Device Charge voltage is set to boost charge level. 0x375E 11/24/2024 08:04:45 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 08:04:45 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 11/24/2024 08:04:45 Device Mains input voltage is no longer out of tolerance. 0x3730 11/24/2024 08:04:45 Device Mains input frequency is no longer out of tolerance. 0x3734 11/24/2024 08:04:40 Device Mains input frequency is out of tolerance. 0x3735 11/24/2024 08:04:40 Device Input is missing a phase. 0x373D 11/24/2024 08:04:40 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/24/2024 08:04:39 Device Charger is off. 0x3765 11/24/2024 08:04:39 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 08:04:39 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 11/24/2024 08:04:39 Device Mains input voltage is out of tolerance. 0x3731 11/24/2024 08:04:29 Device The UPS inverter output is in phase with the bypass input. 0x3721 11/24/2024 08:04:28 Device Static bypass switch is OK and working correctly. 0x37B8 11/24/2024 08:04:28 Device Bypass input is no longer missing a phase. 0x373E 11/24/2024 08:04:27 Device Bypass input voltage is no longer out of tolerance. 0x3736 11/24/2024 08:04:27 Device Bypass input frequency is no longer out of tolerance. 0x373A 11/24/2024 08:04:07 Device The UPS is charging the batteries. 0x37E7 11/24/2024 08:03:58 Device Input is no longer missing a phase. 0x373C 11/24/2024 08:03:57 Device Charge voltage is set to boost charge level. 0x375E 11/24/2024 08:03:57 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 08:03:57 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 11/24/2024 08:03:57 Device Mains input voltage is no longer out of tolerance. 0x3730 11/24/2024 08:03:57 Device Mains input frequency is no longer out of tolerance. 0x3734 11/24/2024 08:03:40 Device Input is missing a phase. 0x373D 11/24/2024 08:03:40 Device Bypass input frequency is out of tolerance. 0x373B 11/24/2024 08:03:40 Device Mains input frequency is out of tolerance. 0x3735 11/24/2024 08:03:39 Device Bypass input is missing a phase. 0x373F 11/24/2024 08:03:39 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/24/2024 08:03:39 Device The UPS inverter output is not in phase with the bypass input. 0x3722 11/24/2024 08:03:39 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 11/24/2024 08:03:39 Device Charger is off. 0x3765 11/24/2024 08:03:39 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 11/24/2024 08:03:39 Device Mains input voltage is out of tolerance. 0x3731 11/24/2024 08:03:39 Device Static bypass switch is OK and working correctly. 0x37B8 11/24/2024 08:03:39 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 11/24/2024 08:03:39 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 11/24/2024 06:35:36 Device UPS time has been changed. 0x3790 11/23/2024 13:37:02 Device Bypass input voltage is no longer out of tolerance. 0x3736 11/23/2024 13:37:02 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 11/23/2024 06:35:35 Device UPS time has been changed. 0x3790 11/22/2024 06:35:35 Device UPS time has been changed. 0x3790 11/21/2024 06:35:36 Device UPS time has been changed. 0x3790 11/20/2024 06:35:36 Device UPS time has been changed. 0x3790 11/19/2024 06:35:35 Device UPS time has been changed. 0x3790 11/18/2024 16:35:53 Device Bypass input voltage is no longer out of tolerance. 0x3736 11/18/2024 16:35:53 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 11/18/2024 06:35:36 Device UPS time has been changed. 0x3790 11/17/2024 06:35:35 Device UPS time has been changed. 0x3790 11/16/2024 06:35:36 Device UPS time has been changed. 0x3790 11/15/2024 19:28:36 Device The UPS inverter output is in phase with the bypass input. 0x3721 11/15/2024 19:28:35 Device The UPS inverter output is not in phase with the bypass input. 0x3722 11/15/2024 19:28:35 Device Bypass input voltage is no longer out of tolerance. 0x3736 11/15/2024 19:28:35 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 11/15/2024 06:35:35 Device UPS time has been changed. 0x3790 11/14/2024 06:35:35 Device UPS time has been changed. 0x3790 11/13/2024 06:35:35 Device UPS time has been changed. 0x3790 11/12/2024 06:35:36 Device UPS time has been changed. 0x3790 11/11/2024 06:35:36 Device UPS time has been changed. 0x3790 11/10/2024 06:35:35 Device UPS time has been changed. 0x3790 11/09/2024 06:35:35 Device UPS time has been changed. 0x3790 11/08/2024 06:35:35 Device UPS time has been changed. 0x3790 11/07/2024 06:35:36 Device UPS time has been changed. 0x3790 11/06/2024 06:35:36 Device UPS time has been changed. 0x3790 11/05/2024 06:35:35 Device UPS time has been changed. 0x3790 11/04/2024 06:35:35 Device UPS time has been changed. 0x3790 11/03/2024 06:35:35 Device UPS time has been changed. 0x3790 11/02/2024 06:35:36 Device UPS time has been changed. 0x3790 11/01/2024 06:35:36 Device UPS time has been changed. 0x3790 10/31/2024 06:35:35 Device UPS time has been changed. 0x3790 10/30/2024 06:35:35 Device UPS time has been changed. 0x3790 10/29/2024 06:35:36 Device UPS time has been changed. 0x3790 10/28/2024 06:35:35 Device UPS time has been changed. 0x3790 10/27/2024 06:35:36 Device UPS time has been changed. 0x3790 10/26/2024 06:35:35 Device UPS time has been changed. 0x3790 10/25/2024 20:53:19 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/25/2024 20:53:19 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/25/2024 06:35:35 Device UPS time has been changed. 0x3790 10/24/2024 06:35:36 Device UPS time has been changed. 0x3790 10/23/2024 06:35:36 Device UPS time has been changed. 0x3790 10/22/2024 06:35:35 Device UPS time has been changed. 0x3790 10/21/2024 06:35:35 Device UPS time has been changed. 0x3790 10/20/2024 06:35:35 Device UPS time has been changed. 0x3790 10/19/2024 06:35:36 Device UPS time has been changed. 0x3790 10/18/2024 06:35:36 Device UPS time has been changed. 0x3790 10/17/2024 06:35:35 Device UPS time has been changed. 0x3790 10/16/2024 06:35:35 Device UPS time has been changed. 0x3790 10/15/2024 06:35:36 Device UPS time has been changed. 0x3790 10/14/2024 06:35:35 Device UPS time has been changed. 0x3790 10/13/2024 15:23:42 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/13/2024 15:23:42 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/13/2024 14:47:13 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/13/2024 14:47:13 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/13/2024 06:35:36 Device UPS time has been changed. 0x3790 10/12/2024 19:56:47 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/12/2024 19:56:47 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/12/2024 19:56:46 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/12/2024 19:56:46 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/12/2024 06:35:35 Device UPS time has been changed. 0x3790 10/11/2024 06:35:36 Device UPS time has been changed. 0x3790 10/10/2024 06:35:36 Device UPS time has been changed. 0x3790 10/09/2024 06:35:35 Device UPS time has been changed. 0x3790 10/08/2024 06:35:35 Device UPS time has been changed. 0x3790 10/07/2024 06:35:36 Device UPS time has been changed. 0x3790 10/06/2024 06:35:36 Device UPS time has been changed. 0x3790 10/06/2024 03:10:31 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/06/2024 03:10:31 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/05/2024 16:30:09 Device Bypass input voltage is no longer out of tolerance. 0x3736 10/05/2024 16:30:09 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 10/05/2024 06:35:35 Device UPS time has been changed. 0x3790 10/04/2024 06:35:35 Device UPS time has been changed. 0x3790 10/03/2024 06:35:35 Device UPS time has been changed. 0x3790 10/02/2024 06:35:35 Device UPS time has been changed. 0x3790 10/01/2024 06:35:36 Device UPS time has been changed. 0x3790 10/01/2024 01:06:00 Device Charge voltage is set to float voltage level. 0x375C 10/01/2024 01:05:00 Device Charge voltage is set to boost charge level. 0x375E 10/01/2024 01:05:00 Device Charge voltage is set to float voltage level. 0x375C 10/01/2024 01:05:00 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 10/01/2024 01:05:00 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 10/01/2024 01:05:00 Device Battery self test is inactive. 0x37D9 10/01/2024 01:05:00 Device Battery capacity is above 75%. 0x37D5 10/01/2024 01:05:00 Device Battery self test has been completed. 0x37DC 10/01/2024 00:05:01 Device Charger is off. 0x3765 10/01/2024 00:05:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 10/01/2024 00:05:01 Device Battery self test is running. 0x37DA 09/30/2024 06:35:35 Device UPS time has been changed. 0x3790 09/29/2024 06:35:36 Device UPS time has been changed. 0x3790 09/28/2024 06:35:35 Device UPS time has been changed. 0x3790 09/27/2024 13:35:51 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/27/2024 13:35:51 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/27/2024 06:35:36 Device UPS time has been changed. 0x3790 09/26/2024 06:35:35 Device UPS time has been changed. 0x3790 09/25/2024 13:31:49 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/25/2024 13:31:48 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/25/2024 13:31:48 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/25/2024 13:31:48 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/25/2024 06:35:35 Device UPS time has been changed. 0x3790 09/24/2024 21:44:37 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 21:43:47 Device The UPS is charging the batteries. 0x37E7 09/24/2024 21:43:38 Device Bypass input is no longer missing a phase. 0x373E 09/24/2024 21:43:38 Device The UPS inverter output is in phase with the bypass input. 0x3721 09/24/2024 21:43:37 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/24/2024 21:43:37 Device Charge voltage is set to boost charge level. 0x375E 09/24/2024 21:43:37 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 21:43:37 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 09/24/2024 21:43:37 Device Mains input voltage is no longer out of tolerance. 0x3730 09/24/2024 21:43:37 Device Static bypass switch is OK and working correctly. 0x37B8 09/24/2024 21:43:37 Device Bypass input is missing a phase. 0x373F 09/24/2024 21:43:37 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 09/24/2024 21:43:37 Device The UPS inverter output is not in phase with the bypass input. 0x3722 09/24/2024 21:43:37 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 09/24/2024 21:43:37 Device Charger is off. 0x3765 09/24/2024 21:43:37 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 09/24/2024 21:43:37 Device Mains input voltage is out of tolerance. 0x3731 09/24/2024 21:43:37 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/24/2024 11:38:25 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 11:37:34 Device The UPS is charging the batteries. 0x37E7 09/24/2024 11:37:27 Device The UPS inverter output is in phase with the bypass input. 0x3721 09/24/2024 11:37:25 Device Bypass input is no longer missing a phase. 0x373E 09/24/2024 11:37:25 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/24/2024 11:37:25 Device Charge voltage is set to boost charge level. 0x375E 09/24/2024 11:37:25 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 11:37:25 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 09/24/2024 11:37:25 Device Mains input voltage is no longer out of tolerance. 0x3730 09/24/2024 11:37:24 Device Static bypass switch is OK and working correctly. 0x37B8 09/24/2024 11:37:24 Device Bypass input is missing a phase. 0x373F 09/24/2024 11:37:24 Device The UPS inverter output is not in phase with the bypass input. 0x3722 09/24/2024 11:37:24 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 09/24/2024 11:37:24 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 09/24/2024 11:37:24 Device Charger is off. 0x3765 09/24/2024 11:37:24 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 09/24/2024 11:37:24 Device Mains input voltage is out of tolerance. 0x3731 09/24/2024 11:37:24 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/24/2024 06:35:36 Device UPS time has been changed. 0x3790 09/23/2024 06:35:36 Device UPS time has been changed. 0x3790 09/23/2024 02:04:01 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/23/2024 02:04:01 Device Static bypass switch is OK and working correctly. 0x37B8 09/23/2024 02:04:01 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 09/23/2024 02:04:01 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/22/2024 06:35:35 Device UPS time has been changed. 0x3790 09/21/2024 06:35:35 Device UPS time has been changed. 0x3790 09/20/2024 06:35:35 Device UPS time has been changed. 0x3790 09/19/2024 06:35:35 Device UPS time has been changed. 0x3790 09/18/2024 18:48:34 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/18/2024 18:48:34 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/18/2024 18:47:04 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/18/2024 18:47:04 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/18/2024 17:45:22 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/18/2024 17:45:21 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/18/2024 15:51:20 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/18/2024 15:51:20 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/18/2024 06:35:36 Device UPS time has been changed. 0x3790 09/17/2024 06:35:35 Device UPS time has been changed. 0x3790 09/16/2024 06:35:36 Device UPS time has been changed. 0x3790 09/15/2024 06:35:35 Device UPS time has been changed. 0x3790 09/14/2024 06:35:35 Device UPS time has been changed. 0x3790 09/13/2024 06:35:36 Device UPS time has been changed. 0x3790 09/12/2024 09:56:30 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/12/2024 09:56:30 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/12/2024 06:35:35 Device UPS time has been changed. 0x3790 09/11/2024 06:35:36 Device UPS time has been changed. 0x3790 09/10/2024 07:27:07 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/10/2024 07:27:07 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/10/2024 06:35:35 Device UPS time has been changed. 0x3790 09/09/2024 06:35:36 Device UPS time has been changed. 0x3790 09/08/2024 06:35:35 Device UPS time has been changed. 0x3790 09/07/2024 06:35:36 Device UPS time has been changed. 0x3790 09/06/2024 06:35:35 Device UPS time has been changed. 0x3790 09/05/2024 20:08:12 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/05/2024 20:08:12 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/05/2024 19:12:37 Device Bypass input voltage is no longer out of tolerance. 0x3736 09/05/2024 19:12:37 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 09/05/2024 06:35:36 Device UPS time has been changed. 0x3790 09/04/2024 06:35:35 Device UPS time has been changed. 0x3790 09/03/2024 06:35:36 Device UPS time has been changed. 0x3790 09/02/2024 06:35:35 Device UPS time has been changed. 0x3790 09/01/2024 06:35:35 Device UPS time has been changed. 0x3790 08/31/2024 15:10:00 Device Charge voltage is set to float voltage level. 0x375C 08/31/2024 15:09:10 Device The UPS is charging the batteries. 0x37E7 08/31/2024 15:09:00 Device Charge voltage is set to boost charge level. 0x375E 08/31/2024 15:09:00 Device Charge voltage is set to float voltage level. 0x375C 08/31/2024 15:09:00 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/31/2024 15:09:00 Device Mains input voltage is no longer out of tolerance. 0x3730 08/31/2024 15:09:00 Device Bypass input voltage is no longer out of tolerance. 0x3736 08/31/2024 15:09:00 Device Static bypass switch is OK and working correctly. 0x37B8 08/31/2024 15:09:00 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 08/31/2024 15:09:00 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 08/31/2024 15:09:00 Device Charger is off. 0x3765 08/31/2024 15:09:00 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/31/2024 15:09:00 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 08/31/2024 15:09:00 Device Mains input voltage is out of tolerance. 0x3731 08/31/2024 06:35:36 Device UPS time has been changed. 0x3790 08/30/2024 10:13:11 Device Charge voltage is set to float voltage level. 0x375C 08/30/2024 10:12:21 Device The UPS is charging the batteries. 0x37E7 08/30/2024 10:12:11 Device Input is no longer missing a phase. 0x373C 08/30/2024 10:12:11 Device Charge voltage is set to boost charge level. 0x375E 08/30/2024 10:12:11 Device Charge voltage is set to float voltage level. 0x375C 08/30/2024 10:12:11 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/30/2024 10:12:11 Device Mains input voltage is no longer out of tolerance. 0x3730 08/30/2024 10:12:11 Device Mains input frequency is no longer out of tolerance. 0x3734 08/30/2024 10:12:10 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 08/30/2024 10:07:34 Device Mains input frequency is out of tolerance. 0x3735 08/30/2024 10:07:34 Device Input is missing a phase. 0x373D 08/30/2024 10:07:34 Device Charger is off. 0x3765 08/30/2024 10:07:34 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/30/2024 10:07:34 Device Mains input voltage is out of tolerance. 0x3731 08/30/2024 06:35:35 Device UPS time has been changed. 0x3790 08/29/2024 06:35:35 Device UPS time has been changed. 0x3790 08/28/2024 06:35:36 Device UPS time has been changed. 0x3790 08/27/2024 06:35:34 Device UPS time has been changed. 0x3790 08/26/2024 23:04:21 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 23:03:31 Device The UPS is charging the batteries. 0x37E7 08/26/2024 23:03:22 Device Input is no longer missing a phase. 0x373C 08/26/2024 23:03:21 Device Charge voltage is set to boost charge level. 0x375E 08/26/2024 23:03:21 Device Charge voltage is set to float voltage level. 0x375C