Network Management Card AOS v6.4.0 Galaxy VM Touch Screen APP v6.4.1 NMC Serial Number: ID1415000438 Date Time Name Contact Location System IP 03/25/2025 11:31:38 UPS 3A COTEL SAS CUARTO ELECTRICO 172.17.3.134 Date Time User Event Code 03/25/2025 11:19:13 Device UPS time has been changed. 0x3790 03/25/2025 12:12:19 Device The UPS is charging the batteries. 0x37E7 03/25/2025 12:11:59 Device Charge voltage is set to boost charge level. 0x375E 03/25/2025 12:11:59 Device Charge voltage is set to float voltage level. 0x375C 03/25/2025 12:11:59 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 03/25/2025 12:11:59 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 03/25/2025 12:11:59 Device The battery state is unknown. Either the battery is new or a battery runtime calibration test has been aborted. 0x37D6 03/25/2025 12:11:59 Device User has cancelled battery self test function. 0x37DE 03/25/2025 12:07:29 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 03/25/2025 12:07:29 Device Charger is off. 0x3765 03/25/2025 12:07:29 Device On battery power in response to a test of the performance of the batteries. 0x3755 03/25/2025 12:07:29 Device Battery self test is running. 0x37DA 03/25/2025 12:07:28 Device User has activated battery self test function. 0x37DD 03/24/2025 16:31:19 Device UPS time has been changed. 0x3790 03/23/2025 16:31:19 Device UPS time has been changed. 0x3790 03/22/2025 16:31:18 Device UPS time has been changed. 0x3790 03/21/2025 16:31:18 Device UPS time has been changed. 0x3790 03/20/2025 16:31:18 Device UPS time has been changed. 0x3790 03/19/2025 16:31:18 Device UPS time has been changed. 0x3790 03/18/2025 16:31:18 Device UPS time has been changed. 0x3790 03/18/2025 13:47:43 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/18/2025 13:47:34 Device Communication between Main Controller and display is fine. 0x370B 03/18/2025 13:47:09 Device Main Controller is unable to communicate with the display. 0x370C 03/17/2025 16:31:18 Device UPS time has been changed. 0x3790 03/16/2025 16:31:19 Device UPS time has been changed. 0x3790 03/15/2025 16:31:18 Device UPS time has been changed. 0x3790 03/14/2025 16:31:18 Device UPS time has been changed. 0x3790 03/13/2025 16:31:18 Device UPS time has been changed. 0x3790 03/12/2025 16:31:18 Device UPS time has been changed. 0x3790 03/12/2025 11:42:51 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/12/2025 11:42:41 Device Communication between Main Controller and display is fine. 0x370B 03/12/2025 11:42:18 Device Main Controller is unable to communicate with the display. 0x370C 03/11/2025 16:31:15 Device UPS time has been changed. 0x3790 03/11/2025 16:27:14 Device Communication to parallel UPS 1 is obtained. 0x377C 03/11/2025 16:27:12 Device PBUS cable 2 is fine. 0x3772 03/11/2025 16:27:12 Device PBUS cable 1 is fine. 0x3770 03/10/2025 16:31:14 Device UPS time has been changed. 0x3790 03/09/2025 16:31:15 Device UPS time has been changed. 0x3790 03/08/2025 16:31:36 Device UPS time has been changed. 0x3790 03/07/2025 10:16:56 Device Main Controller is unable to communicate with parallel UPS 1. The UPS might have been powered down or communication cables may be damaged. 0x377D 03/07/2025 10:16:55 Device PBUS cable 2 may be damaged. 0x3773 03/07/2025 10:16:55 Device PBUS cable 1 may be damaged. 0x3771 03/07/2025 10:14:52 Device The UPS is synchronized to the bypass input. 0x3711 03/07/2025 09:45:47 Device UPS time has been changed. 0x3790 03/06/2025 16:35:19 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 03/06/2025 16:35:19 Device The user has requested a transfer to inverter. 0x37AE 03/06/2025 16:35:17 Device The output voltage is no longer out of tolerance. 0x3728 03/06/2025 16:35:16 Device Output frequency is no longer out of tolerance. 0x372A 03/06/2025 16:35:16 Device The UPS is synchronized to the parallel system. 0x3727 03/06/2025 16:35:16 Device Unit output breaker UOB is closed. 0x37C2 03/06/2025 16:34:36 Device Modular battery cabinet 1 is ok. 0x37EE 03/06/2025 16:34:35 Device Modular battery cabinet 1 breaker 2 is closed. 0x37CE 03/06/2025 16:33:48 Device Modular battery cabinet 1 breaker 1 is closed. 0x37CE 03/06/2025 16:32:53 Device Modular battery cabinet 2 is ok. 0x37EE 03/06/2025 16:32:53 Device Modular battery cabinet 2 breaker 2 is closed. 0x37CE 03/06/2025 16:32:40 Device Modular battery cabinet 2 breaker 1 is closed. 0x37CE 03/06/2025 16:32:31 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 03/06/2025 16:32:27 Device The battery runtime is above configured minimum acceptable value. 0x37E5 03/06/2025 16:32:04 Device Modular battery cabinet 3 is ok. 0x37EE 03/06/2025 16:32:03 Device Modular battery cabinet 3 breaker 1 is closed. 0x37CE 03/06/2025 16:31:55 Device Modular battery cabinet 2 breaker 1 is closed. 0x37CE 03/06/2025 16:31:47 Device Static bypass switch is OK and working correctly. 0x37B8 03/06/2025 16:31:41 Device The UPS inverter output is in phase with the bypass input. 0x3721 03/06/2025 16:31:41 Device The UPS is synchronized to the bypass input. 0x3711 03/06/2025 16:31:41 Device Bypass input is no longer missing a phase. 0x373E 03/06/2025 16:31:40 Device Bypass input voltage is no longer out of tolerance. 0x3736 03/06/2025 16:31:40 Device Bypass input frequency is no longer out of tolerance. 0x373A 03/06/2025 16:31:40 Device Bypass static switch input breaker SSIB is closed. 0x37C8 03/06/2025 16:30:40 Device The battery runtime is below configured minimum acceptable value. 0x37E6 03/06/2025 16:30:24 Device Battery is working correctly. 0x37D0 03/06/2025 16:30:20 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 03/06/2025 16:30:19 Device The load is supplied from the inverters of the system. One or more UPS is in normal or battery operation. 0x3761 03/06/2025 16:30:17 Device Static bypass switch is inoperable. UPS is prevented from going into static bypass operation. 0x37BA 03/06/2025 16:30:17 Device Bypass input frequency is out of tolerance. 0x373B 03/06/2025 16:30:17 Device Output frequency is out of tolerance. 0x372B 03/06/2025 16:30:17 Device The UPS is charging the batteries. 0x37E7 03/06/2025 16:30:17 Device Charge voltage is set to float voltage level. 0x375C 03/06/2025 16:30:17 Device The output power is turned off. 0x3756 03/06/2025 16:30:17 Device Charger is off. 0x3765 03/06/2025 16:30:17 Device Self test is passed. 0x0105 03/06/2025 16:30:17 Device Surveillance OK. 0x3780 03/06/2025 16:30:05 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 03/06/2025 16:30:05 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 03/06/2025 16:30:05 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 03/06/2025 16:30:05 Device Modular battery cabinet 1 breaker 1 is open. 0x37CF 03/06/2025 16:30:04 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 03/06/2025 16:30:03 Device All UPS fans are OK. 0x3784 03/06/2025 16:29:58 Device UPS has one or more inoperable fans. Fan redundancy is lost. 0x3785 03/06/2025 16:29:55 Device The battery state is unknown. Either the battery is new or a battery runtime calibration test has been aborted. 0x37D6 03/06/2025 16:29:55 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 03/06/2025 16:29:55 Device The output voltage is out of tolerance. 0x3729 03/06/2025 16:29:55 Device Bypass input is missing a phase. 0x373F 03/06/2025 16:29:55 Device Battery is not working correctly. 0x37D1 03/06/2025 16:29:55 Device Surveillance detected fault. 0x3781 03/06/2025 16:29:55 Device Modular battery cabinet 3 is not working correctly. 0x37EF 03/06/2025 16:29:55 Device Modular battery cabinet 2 is not working correctly. 0x37EF 03/06/2025 16:29:55 Device Modular battery cabinet 1 is not working correctly. 0x37EF 03/06/2025 16:29:55 Device Not enough UPS units ready to turn on inverter cleared. 0x3778 03/06/2025 16:29:55 Device The system output power is turned off. 0x3760 03/06/2025 16:29:55 Device Unit output breaker UOB is open, and UPS cannot feed the load. 0x37C3 03/06/2025 16:29:55 Device Bypass static switch input breaker SSIB is open, making static bypass operation unavailable. 0x37C9 03/06/2025 16:29:55 Device The UPS inverter output is not in phase with the bypass input. 0x3722 03/06/2025 16:29:55 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 03/06/2025 16:29:55 Device Controller has booted and is ready to run. 0x3701 03/03/2025 10:53:43 Device Charger is off. 0x3765 03/03/2025 10:53:41 Device Surveillance detected fault. 0x3781 03/03/2025 10:53:39 Device Charge voltage is set to float voltage level. 0x375C 03/03/2025 10:53:38 Device Mains input frequency is out of tolerance. 0x3735 03/03/2025 10:53:37 Device Input is missing a phase. 0x373D 03/03/2025 10:53:36 Device Battery is not working correctly. 0x37D1 03/03/2025 10:53:36 Device Charger is off. 0x3765 03/03/2025 10:53:36 Device Mains input voltage is out of tolerance. 0x3731 03/03/2025 10:53:36 Device Unit input breaker UIB is open, and the UPS is prevented from running in normal operation. 0x37C1 03/03/2025 10:53:19 Device Modular battery cabinet 3 is not working correctly. 0x37EF 03/03/2025 10:53:19 Device Modular battery cabinet 3 breaker 1 is open. 0x37CF 03/03/2025 10:53:09 Device Modular battery cabinet 2 breaker 1 is open. 0x37CF 03/03/2025 10:53:06 Device Modular battery cabinet 2 is not working correctly. 0x37EF 03/03/2025 10:53:05 Device Modular battery cabinet 2 breaker 2 is open. 0x37CF 03/03/2025 10:52:55 Device Modular battery cabinet 1 breaker 1 is open. 0x37CF 03/03/2025 10:52:51 Device Modular battery cabinet 1 is not working correctly. 0x37EF 03/03/2025 10:52:51 Device Modular battery cabinet 1 breaker 2 is open. 0x37CF 03/03/2025 10:52:37 Device Output frequency is out of tolerance. 0x372B 03/03/2025 10:52:37 Device Bypass input frequency is out of tolerance. 0x373B 03/03/2025 10:52:37 Device Static bypass switch needs a technical check but is still fully operational. 0x37B9 03/03/2025 10:52:36 Device Bypass input is missing a phase. 0x373F 03/03/2025 10:52:36 Device Static bypass switch is inoperable. UPS is prevented from going into static bypass operation. 0x37BA 03/03/2025 10:52:36 Device The inverter is no longer off due to a request by the user. 0x37B5 03/03/2025 10:52:36 Device The output power is turned off. 0x3756 03/03/2025 10:52:36 Device The UPS inverter output is not in phase with the bypass input. 0x3722 03/03/2025 10:52:36 Device The UPS is unable to synchronize to the bypass input, external source or parallel system. 0x3713 03/03/2025 10:52:36 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 03/03/2025 10:52:36 Device The output voltage is out of tolerance. 0x3729 03/03/2025 10:52:36 Device Bypass static switch input breaker SSIB is open, making static bypass operation unavailable. 0x37C9 03/03/2025 10:52:28 Device The output voltage is no longer out of tolerance. 0x3728 03/03/2025 10:52:28 Device The UPS is synchronized to the bypass input. 0x3711 03/03/2025 10:52:28 Device The UPS is in bypass in response to a critical event or an inverter off request. 0x3753 03/03/2025 10:52:28 Device Unit output breaker UOB is open, and UPS cannot feed the load. 0x37C3 03/03/2025 10:52:28 Device The output voltage is out of tolerance. 0x3729 03/03/2025 10:51:36 Device The UPS is ready to enter static bypass but awaits permission from the system. UPS output is off. 0x3758 03/03/2025 10:51:36 Device The inverter is off due to a request by the user. 0x37B6 03/03/2025 10:51:36 Device The user has requested to turn off the inverter. 0x37AF 03/03/2025 09:45:48 Device UPS time has been changed. 0x3790 03/02/2025 09:45:48 Device UPS time has been changed. 0x3790 03/01/2025 09:45:48 Device UPS time has been changed. 0x3790 02/28/2025 09:45:49 Device UPS time has been changed. 0x3790 02/27/2025 09:45:48 Device UPS time has been changed. 0x3790 02/26/2025 15:23:39 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 02/26/2025 15:23:30 Device Communication between Main Controller and display is fine. 0x370B 02/26/2025 15:23:06 Device Main Controller is unable to communicate with the display. 0x370C 02/26/2025 09:45:48 Device UPS time has been changed. 0x3790 02/25/2025 09:45:48 Device UPS time has been changed. 0x3790 02/24/2025 09:45:47 Device UPS time has been changed. 0x3790 02/23/2025 09:45:49 Device UPS time has been changed. 0x3790 02/23/2025 08:49:10 Device Charge voltage is set to float voltage level. 0x375C 02/23/2025 08:48:30 Device The UPS is charging the batteries. 0x37E7 02/23/2025 08:48:11 Device Input is no longer missing a phase. 0x373C 02/23/2025 08:48:10 Device Charge voltage is set to boost charge level. 0x375E 02/23/2025 08:48:10 Device Charge voltage is set to float voltage level. 0x375C 02/23/2025 08:48:10 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/23/2025 08:48:10 Device Mains input voltage is no longer out of tolerance. 0x3730 02/23/2025 08:48:10 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:44:28 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:44:28 Device Input is missing a phase. 0x373D 02/23/2025 08:44:28 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 02/23/2025 08:44:28 Device Charger is off. 0x3765 02/23/2025 08:44:28 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 02/23/2025 08:44:28 Device Mains input voltage is out of tolerance. 0x3731 02/23/2025 08:43:04 Device Charge voltage is set to float voltage level. 0x375C 02/23/2025 08:42:24 Device The UPS is charging the batteries. 0x37E7 02/23/2025 08:42:05 Device Input is no longer missing a phase. 0x373C 02/23/2025 08:42:04 Device Charge voltage is set to boost charge level. 0x375E 02/23/2025 08:42:04 Device Charge voltage is set to float voltage level. 0x375C 02/23/2025 08:42:04 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/23/2025 08:42:04 Device Mains input voltage is no longer out of tolerance. 0x3730 02/23/2025 08:42:04 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:40:53 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:40:53 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:40:46 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:40:46 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:40:04 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:40:03 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:39:34 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:39:34 Device Input is missing a phase. 0x373D 02/23/2025 08:39:33 Device Charger is off. 0x3765 02/23/2025 08:39:33 Device Charge voltage is set to float voltage level. 0x375C 02/23/2025 08:39:33 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 02/23/2025 08:39:33 Device Mains input voltage is out of tolerance. 0x3731 02/23/2025 08:39:23 Device Input is no longer missing a phase. 0x373C 02/23/2025 08:39:23 Device Charge voltage is set to boost charge level. 0x375E 02/23/2025 08:39:23 Device Charge voltage is set to float voltage level. 0x375C 02/23/2025 08:39:23 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/23/2025 08:39:23 Device Mains input voltage is no longer out of tolerance. 0x3730 02/23/2025 08:39:23 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:38:58 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:38:58 Device Mains input frequency is no longer out of tolerance. 0x3734 02/23/2025 08:38:44 Device Mains input frequency is out of tolerance. 0x3735 02/23/2025 08:38:44 Device Input is missing a phase. 0x373D 02/23/2025 08:38:43 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 02/23/2025 08:38:43 Device Charger is off. 0x3765 02/23/2025 08:38:43 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 02/23/2025 08:38:43 Device Mains input voltage is out of tolerance. 0x3731 02/22/2025 09:45:48 Device UPS time has been changed. 0x3790 02/21/2025 09:45:48 Device UPS time has been changed. 0x3790 02/20/2025 12:29:13 Device Bypass input voltage is no longer out of tolerance. 0x3736 02/20/2025 12:29:13 Device Bypass input voltage is out of tolerance and UPS is prevented from going into requested bypass mode. 0x3737 02/20/2025 09:45:48 Device UPS time has been changed. 0x3790 02/19/2025 09:45:48 Device UPS time has been changed. 0x3790 02/18/2025 09:45:49 Device UPS time has been changed. 0x3790 02/18/2025 08:52:09 Device Charge voltage is set to float voltage level. 0x375C 02/18/2025 00:47:55 Device The UPS is charging the batteries. 0x37E7 02/18/2025 00:47:35 Device Charge voltage is set to boost charge level. 0x375E 02/18/2025 00:47:35 Device Charge voltage is set to float voltage level. 0x375C 02/18/2025 00:47:35 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 02/18/2025 00:47:35 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 02/18/2025 00:47:35 Device Battery self test is inactive. 0x37D9 02/18/2025 00:47:35 Device Battery capacity is above 75%. 0x37D5 02/18/2025 00:47:35 Device Battery self test has been completed. 0x37DC 02/18/2025 00:00:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 02/18/2025 00:00:01 Device Charger is off. 0x3765 02/18/2025 00:00:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 02/18/2025 00:00:01 Device Battery self test is running. 0x37DA 02/17/2025 09:45:48 Device UPS time has been changed. 0x3790 02/16/2025 09:45:48 Device UPS time has been changed. 0x3790 02/15/2025 09:45:48 Device UPS time has been changed. 0x3790 02/14/2025 09:45:48 Device UPS time has been changed. 0x3790 02/13/2025 09:45:48 Device UPS time has been changed. 0x3790 02/12/2025 09:45:48 Device UPS time has been changed. 0x3790 02/11/2025 09:45:48 Device UPS time has been changed. 0x3790 02/10/2025 09:45:48 Device UPS time has been changed. 0x3790 02/09/2025 09:45:49 Device UPS time has been changed. 0x3790 02/08/2025 09:45:47 Device UPS time has been changed. 0x3790 02/07/2025 09:45:48 Device UPS time has been changed. 0x3790 02/06/2025 09:45:48 Device UPS time has been changed. 0x3790 02/05/2025 09:45:49 Device UPS time has been changed. 0x3790 02/04/2025 09:45:48 Device UPS time has been changed. 0x3790 02/03/2025 09:45:48 Device UPS time has been changed. 0x3790 02/02/2025 09:45:47 Device UPS time has been changed. 0x3790 02/01/2025 09:45:48 Device UPS time has been changed. 0x3790 01/31/2025 09:45:49 Device UPS time has been changed. 0x3790 01/30/2025 09:45:48 Device UPS time has been changed. 0x3790 01/29/2025 09:45:48 Device UPS time has been changed. 0x3790 01/28/2025 09:45:48 Device UPS time has been changed. 0x3790 01/27/2025 18:23:27 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 18:22:47 Device The UPS is charging the batteries. 0x37E7 01/27/2025 18:22:28 Device Input is no longer missing a phase. 0x373C 01/27/2025 18:22:27 Device Charge voltage is set to boost charge level. 0x375E 01/27/2025 18:22:27 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 18:22:27 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 01/27/2025 18:22:27 Device Mains input voltage is no longer out of tolerance. 0x3730 01/27/2025 18:22:27 Device Mains input frequency is no longer out of tolerance. 0x3734 01/27/2025 18:22:23 Device Mains input frequency is out of tolerance. 0x3735 01/27/2025 18:22:22 Device Input is missing a phase. 0x373D 01/27/2025 18:22:22 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 01/27/2025 18:22:22 Device Charger is off. 0x3765 01/27/2025 18:22:22 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 01/27/2025 18:22:22 Device Mains input voltage is out of tolerance. 0x3731 01/27/2025 18:04:15 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 18:03:35 Device The UPS is charging the batteries. 0x37E7 01/27/2025 18:03:16 Device Input is no longer missing a phase. 0x373C 01/27/2025 18:03:15 Device Charge voltage is set to boost charge level. 0x375E 01/27/2025 18:03:15 Device Charge voltage is set to float voltage level. 0x375C 01/27/2025 18:03:15 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 01/27/2025 18:03:15 Device Mains input voltage is no longer out of tolerance. 0x3730 01/27/2025 18:03:15 Device Mains input frequency is no longer out of tolerance. 0x3734 01/27/2025 17:57:41 Device The UPS inverter output is in phase with the bypass input. 0x3721 01/27/2025 17:57:40 Device The UPS inverter output is not in phase with the bypass input. 0x3722 01/27/2025 17:57:08 Device Mains input frequency is out of tolerance. 0x3735 01/27/2025 17:57:08 Device Input is missing a phase. 0x373D 01/27/2025 17:57:07 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 01/27/2025 17:57:07 Device Charger is off. 0x3765 01/27/2025 17:57:07 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 01/27/2025 17:57:07 Device Mains input voltage is out of tolerance. 0x3731 01/27/2025 09:45:49 Device UPS time has been changed. 0x3790 01/26/2025 09:45:48 Device UPS time has been changed. 0x3790 01/25/2025 09:45:47 Device UPS time has been changed. 0x3790 01/24/2025 09:45:48 Device UPS time has been changed. 0x3790 01/23/2025 09:45:49 Device UPS time has been changed. 0x3790 01/22/2025 09:45:48 Device UPS time has been changed. 0x3790 01/21/2025 09:45:48 Device UPS time has been changed. 0x3790 01/20/2025 09:45:48 Device UPS time has been changed. 0x3790 01/19/2025 09:45:47 Device UPS time has been changed. 0x3790 01/18/2025 09:45:49 Device UPS time has been changed. 0x3790 01/17/2025 09:45:49 Device UPS time has been changed. 0x3790 01/16/2025 09:45:47 Device UPS time has been changed. 0x3790 01/15/2025 09:45:49 Device UPS time has been changed. 0x3790 01/14/2025 09:45:47 Device UPS time has been changed. 0x3790 01/13/2025 09:45:49 Device UPS time has been changed. 0x3790 01/12/2025 09:45:48 Device UPS time has been changed. 0x3790 01/11/2025 09:45:48 Device UPS time has been changed. 0x3790 01/10/2025 09:45:48 Device UPS time has been changed. 0x3790 01/09/2025 09:45:49 Device UPS time has been changed. 0x3790 01/08/2025 09:45:48 Device UPS time has been changed. 0x3790 01/07/2025 09:45:49 Device UPS time has been changed. 0x3790 01/06/2025 09:45:48 Device UPS time has been changed. 0x3790 01/05/2025 09:45:47 Device UPS time has been changed. 0x3790 01/04/2025 09:45:49 Device UPS time has been changed. 0x3790 01/03/2025 09:45:48 Device UPS time has been changed. 0x3790 01/02/2025 09:45:48 Device UPS time has been changed. 0x3790 01/01/2025 09:45:48 Device UPS time has been changed. 0x3790 12/31/2024 09:45:49 Device UPS time has been changed. 0x3790 12/30/2024 09:45:48 Device UPS time has been changed. 0x3790 12/29/2024 09:45:48 Device UPS time has been changed. 0x3790 12/28/2024 09:45:47 Device UPS time has been changed. 0x3790 12/27/2024 09:45:48 Device UPS time has been changed. 0x3790 12/26/2024 09:45:49 Device UPS time has been changed. 0x3790 12/25/2024 09:45:48 Device UPS time has been changed. 0x3790 12/24/2024 09:45:48 Device UPS time has been changed. 0x3790 12/23/2024 09:45:47 Device UPS time has been changed. 0x3790 12/22/2024 09:45:49 Device UPS time has been changed. 0x3790 12/21/2024 09:45:48 Device UPS time has been changed. 0x3790 12/20/2024 09:45:48 Device UPS time has been changed. 0x3790 12/19/2024 09:45:48 Device UPS time has been changed. 0x3790 12/18/2024 09:45:48 Device UPS time has been changed. 0x3790 12/17/2024 09:45:49 Device UPS time has been changed. 0x3790 12/17/2024 01:29:23 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 01:28:43 Device The UPS is charging the batteries. 0x37E7 12/17/2024 01:28:24 Device Input is no longer missing a phase. 0x373C 12/17/2024 01:28:23 Device Charge voltage is set to boost charge level. 0x375E 12/17/2024 01:28:23 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 01:28:23 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/17/2024 01:28:23 Device Mains input voltage is no longer out of tolerance. 0x3730 12/17/2024 01:28:23 Device Mains input frequency is no longer out of tolerance. 0x3734 12/17/2024 01:28:18 Device Mains input frequency is out of tolerance. 0x3735 12/17/2024 01:28:18 Device Input is missing a phase. 0x373D 12/17/2024 01:28:18 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/17/2024 01:28:18 Device Charger is off. 0x3765 12/17/2024 01:28:18 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/17/2024 01:28:18 Device Mains input voltage is out of tolerance. 0x3731 12/17/2024 01:14:13 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/17/2024 01:14:10 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/17/2024 00:19:10 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 00:18:30 Device The UPS is charging the batteries. 0x37E7 12/17/2024 00:18:10 Device Input is no longer missing a phase. 0x373C 12/17/2024 00:18:10 Device Charge voltage is set to boost charge level. 0x375E 12/17/2024 00:18:10 Device Charge voltage is set to float voltage level. 0x375C 12/17/2024 00:18:10 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/17/2024 00:18:10 Device Mains input voltage is no longer out of tolerance. 0x3730 12/17/2024 00:18:10 Device Mains input frequency is no longer out of tolerance. 0x3734 12/17/2024 00:18:00 Device Mains input frequency is out of tolerance. 0x3735 12/17/2024 00:18:00 Device Mains input frequency is no longer out of tolerance. 0x3734 12/17/2024 00:06:21 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/17/2024 00:06:18 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/17/2024 00:05:48 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/17/2024 00:05:48 Device The battery state is unknown. Either the battery is new or a battery runtime calibration test has been aborted. 0x37D6 12/17/2024 00:05:48 Device Battery self test has been aborted due to a critical alarm. 0x37DB 12/17/2024 00:05:47 Device Mains input frequency is out of tolerance. 0x3735 12/17/2024 00:05:47 Device Input is missing a phase. 0x373D 12/17/2024 00:05:47 Device Mains input voltage is out of tolerance. 0x3731 12/17/2024 00:00:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/17/2024 00:00:01 Device Charger is off. 0x3765 12/17/2024 00:00:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 12/17/2024 00:00:01 Device Battery self test is running. 0x37DA 12/16/2024 09:45:48 Device UPS time has been changed. 0x3790 12/15/2024 09:45:48 Device UPS time has been changed. 0x3790 12/14/2024 09:45:47 Device UPS time has been changed. 0x3790 12/13/2024 09:45:49 Device UPS time has been changed. 0x3790 12/13/2024 07:22:23 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 07:21:43 Device The UPS is charging the batteries. 0x37E7 12/13/2024 07:21:24 Device Input is no longer missing a phase. 0x373C 12/13/2024 07:21:23 Device Charge voltage is set to boost charge level. 0x375E 12/13/2024 07:21:23 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 07:21:23 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/13/2024 07:21:23 Device Mains input voltage is no longer out of tolerance. 0x3730 12/13/2024 07:21:23 Device Mains input frequency is no longer out of tolerance. 0x3734 12/13/2024 07:21:18 Device Mains input frequency is out of tolerance. 0x3735 12/13/2024 07:21:18 Device Input is missing a phase. 0x373D 12/13/2024 07:21:17 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/13/2024 07:21:17 Device Charger is off. 0x3765 12/13/2024 07:21:17 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/13/2024 07:21:17 Device Mains input voltage is out of tolerance. 0x3731 12/13/2024 07:20:42 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 07:20:02 Device The UPS is charging the batteries. 0x37E7 12/13/2024 07:19:43 Device Input is no longer missing a phase. 0x373C 12/13/2024 07:19:42 Device Charge voltage is set to boost charge level. 0x375E 12/13/2024 07:19:42 Device Charge voltage is set to float voltage level. 0x375C 12/13/2024 07:19:42 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/13/2024 07:19:42 Device Mains input voltage is no longer out of tolerance. 0x3730 12/13/2024 07:19:42 Device Mains input frequency is no longer out of tolerance. 0x3734 12/13/2024 07:19:37 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/13/2024 07:19:32 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/13/2024 07:19:01 Device Mains input frequency is out of tolerance. 0x3735 12/13/2024 07:19:01 Device Input is missing a phase. 0x373D 12/13/2024 07:19:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/13/2024 07:19:01 Device Charger is off. 0x3765 12/13/2024 07:19:01 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/13/2024 07:19:01 Device Mains input voltage is out of tolerance. 0x3731 12/12/2024 09:45:48 Device UPS time has been changed. 0x3790 12/12/2024 04:39:58 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 04:39:18 Device The UPS is charging the batteries. 0x37E7 12/12/2024 04:38:59 Device Input is no longer missing a phase. 0x373C 12/12/2024 04:38:58 Device Charge voltage is set to boost charge level. 0x375E 12/12/2024 04:38:58 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 04:38:58 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/12/2024 04:38:58 Device Mains input voltage is no longer out of tolerance. 0x3730 12/12/2024 04:38:58 Device Mains input frequency is no longer out of tolerance. 0x3734 12/12/2024 04:38:54 Device Mains input frequency is out of tolerance. 0x3735 12/12/2024 04:38:54 Device Input is missing a phase. 0x373D 12/12/2024 04:38:53 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/12/2024 04:38:53 Device Charger is off. 0x3765 12/12/2024 04:38:53 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/12/2024 04:38:53 Device Mains input voltage is out of tolerance. 0x3731 12/12/2024 03:54:33 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 03:54:31 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 03:54:15 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 03:54:13 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 03:48:50 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 03:48:49 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 03:48:49 Device The UPS inverter output is in phase with the bypass input. 0x3721 12/12/2024 03:48:48 Device The UPS inverter output is not in phase with the bypass input. 0x3722 12/12/2024 03:26:45 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 03:26:05 Device The UPS is charging the batteries. 0x37E7 12/12/2024 03:25:46 Device Input is no longer missing a phase. 0x373C 12/12/2024 03:25:45 Device Charge voltage is set to boost charge level. 0x375E 12/12/2024 03:25:45 Device Charge voltage is set to float voltage level. 0x375C 12/12/2024 03:25:45 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 12/12/2024 03:25:45 Device Mains input voltage is no longer out of tolerance. 0x3730 12/12/2024 03:25:45 Device Mains input frequency is no longer out of tolerance. 0x3734 12/12/2024 03:25:04 Device Mains input frequency is out of tolerance. 0x3735 12/12/2024 03:25:03 Device Input is missing a phase. 0x373D 12/12/2024 03:25:03 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 12/12/2024 03:25:03 Device Charger is off. 0x3765 12/12/2024 03:25:03 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 12/12/2024 03:25:03 Device Mains input voltage is out of tolerance. 0x3731 12/11/2024 09:45:48 Device UPS time has been changed. 0x3790 12/10/2024 09:45:48 Device UPS time has been changed. 0x3790 12/09/2024 09:45:48 Device UPS time has been changed. 0x3790 12/08/2024 09:45:49 Device UPS time has been changed. 0x3790 12/07/2024 09:45:48 Device UPS time has been changed. 0x3790 12/06/2024 09:45:48 Device UPS time has been changed. 0x3790 12/05/2024 09:45:48 Device UPS time has been changed. 0x3790 12/04/2024 09:45:49 Device UPS time has been changed. 0x3790 12/03/2024 09:45:48 Device UPS time has been changed. 0x3790 12/02/2024 09:45:48 Device UPS time has been changed. 0x3790 12/01/2024 09:45:48 Device UPS time has been changed. 0x3790 11/30/2024 09:45:48 Device UPS time has been changed. 0x3790 11/29/2024 09:45:49 Device UPS time has been changed. 0x3790 11/28/2024 09:45:47 Device UPS time has been changed. 0x3790 11/27/2024 09:45:48 Device UPS time has been changed. 0x3790 11/26/2024 09:45:48 Device UPS time has been changed. 0x3790 11/25/2024 09:45:49 Device UPS time has been changed. 0x3790 11/24/2024 09:45:48 Device UPS time has been changed. 0x3790 11/24/2024 07:11:25 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 07:10:45 Device The UPS is charging the batteries. 0x37E7 11/24/2024 07:10:26 Device Input is no longer missing a phase. 0x373C 11/24/2024 07:10:25 Device Charge voltage is set to boost charge level. 0x375E 11/24/2024 07:10:25 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 07:10:25 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 11/24/2024 07:10:25 Device Mains input voltage is no longer out of tolerance. 0x3730 11/24/2024 07:10:25 Device Mains input frequency is no longer out of tolerance. 0x3734 11/24/2024 07:10:20 Device Mains input frequency is out of tolerance. 0x3735 11/24/2024 07:10:20 Device Input is missing a phase. 0x373D 11/24/2024 07:10:20 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/24/2024 07:10:20 Device Charger is off. 0x3765 11/24/2024 07:10:20 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 11/24/2024 07:10:20 Device Mains input voltage is out of tolerance. 0x3731 11/24/2024 07:10:09 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 07:09:29 Device The UPS is charging the batteries. 0x37E7 11/24/2024 07:09:10 Device Input is no longer missing a phase. 0x373C 11/24/2024 07:09:09 Device Charge voltage is set to boost charge level. 0x375E 11/24/2024 07:09:09 Device Charge voltage is set to float voltage level. 0x375C 11/24/2024 07:09:09 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 11/24/2024 07:09:09 Device Mains input voltage is no longer out of tolerance. 0x3730 11/24/2024 07:09:09 Device Mains input frequency is no longer out of tolerance. 0x3734 11/24/2024 07:08:28 Device Input is missing a phase. 0x373D 11/24/2024 07:08:28 Device Mains input frequency is out of tolerance. 0x3735 11/24/2024 07:08:27 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 11/24/2024 07:08:27 Device Charger is off. 0x3765 11/24/2024 07:08:27 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 11/24/2024 07:08:27 Device Mains input voltage is out of tolerance. 0x3731 11/23/2024 09:45:48 Device UPS time has been changed. 0x3790 11/22/2024 09:45:48 Device UPS time has been changed. 0x3790 11/21/2024 09:45:48 Device UPS time has been changed. 0x3790 11/20/2024 09:45:48 Device UPS time has been changed. 0x3790 11/19/2024 09:45:48 Device UPS time has been changed. 0x3790 11/18/2024 09:45:48 Device UPS time has been changed. 0x3790 11/17/2024 09:45:48 Device UPS time has been changed. 0x3790 11/16/2024 09:45:49 Device UPS time has been changed. 0x3790 11/15/2024 09:45:48 Device UPS time has been changed. 0x3790 11/14/2024 09:45:48 Device UPS time has been changed. 0x3790 11/13/2024 09:45:47 Device UPS time has been changed. 0x3790 11/12/2024 09:45:48 Device UPS time has been changed. 0x3790 11/11/2024 09:45:49 Device UPS time has been changed. 0x3790 11/10/2024 09:45:48 Device UPS time has been changed. 0x3790 11/09/2024 09:45:47 Device UPS time has been changed. 0x3790 11/08/2024 09:45:49 Device UPS time has been changed. 0x3790 11/07/2024 09:45:47 Device UPS time has been changed. 0x3790 11/06/2024 09:45:49 Device UPS time has been changed. 0x3790 11/05/2024 09:45:48 Device UPS time has been changed. 0x3790 11/04/2024 09:45:48 Device UPS time has been changed. 0x3790 11/03/2024 09:45:47 Device UPS time has been changed. 0x3790 11/02/2024 09:45:49 Device UPS time has been changed. 0x3790 11/01/2024 09:45:48 Device UPS time has been changed. 0x3790 10/31/2024 09:45:47 Device UPS time has been changed. 0x3790 10/30/2024 09:45:48 Device UPS time has been changed. 0x3790 10/29/2024 09:45:48 Device UPS time has been changed. 0x3790 10/28/2024 09:45:49 Device UPS time has been changed. 0x3790 10/27/2024 09:45:48 Device UPS time has been changed. 0x3790 10/26/2024 09:45:47 Device UPS time has been changed. 0x3790 10/25/2024 09:45:48 Device UPS time has been changed. 0x3790 10/24/2024 09:45:49 Device UPS time has been changed. 0x3790 10/23/2024 09:45:48 Device UPS time has been changed. 0x3790 10/22/2024 09:45:47 Device UPS time has been changed. 0x3790 10/21/2024 09:45:48 Device UPS time has been changed. 0x3790 10/20/2024 09:45:48 Device UPS time has been changed. 0x3790 10/19/2024 09:45:48 Device UPS time has been changed. 0x3790 10/18/2024 09:45:48 Device UPS time has been changed. 0x3790 10/17/2024 09:45:48 Device UPS time has been changed. 0x3790 10/16/2024 09:45:48 Device UPS time has been changed. 0x3790 10/15/2024 09:45:49 Device UPS time has been changed. 0x3790 10/15/2024 08:54:59 Device Charge voltage is set to float voltage level. 0x375C 10/15/2024 00:47:56 Device The UPS is charging the batteries. 0x37E7 10/15/2024 00:47:36 Device Charge voltage is set to boost charge level. 0x375E 10/15/2024 00:47:36 Device Charge voltage is set to float voltage level. 0x375C 10/15/2024 00:47:36 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 10/15/2024 00:47:36 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 10/15/2024 00:47:36 Device Battery self test is inactive. 0x37D9 10/15/2024 00:47:36 Device Battery capacity is above 75%. 0x37D5 10/15/2024 00:47:36 Device Battery self test has been completed. 0x37DC 10/15/2024 00:00:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 10/15/2024 00:00:01 Device Charger is off. 0x3765 10/15/2024 00:00:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 10/15/2024 00:00:01 Device Battery self test is running. 0x37DA 10/14/2024 09:45:48 Device UPS time has been changed. 0x3790 10/13/2024 09:45:48 Device UPS time has been changed. 0x3790 10/12/2024 09:45:48 Device UPS time has been changed. 0x3790 10/11/2024 09:45:47 Device UPS time has been changed. 0x3790 10/10/2024 09:45:49 Device UPS time has been changed. 0x3790 10/09/2024 09:45:48 Device UPS time has been changed. 0x3790 10/08/2024 09:45:48 Device UPS time has been changed. 0x3790 10/07/2024 09:45:48 Device UPS time has been changed. 0x3790 10/06/2024 09:45:49 Device UPS time has been changed. 0x3790 10/05/2024 09:45:48 Device UPS time has been changed. 0x3790 10/04/2024 09:45:48 Device UPS time has been changed. 0x3790 10/03/2024 09:45:48 Device UPS time has been changed. 0x3790 10/02/2024 09:45:48 Device UPS time has been changed. 0x3790 10/01/2024 09:45:49 Device UPS time has been changed. 0x3790 09/30/2024 09:45:47 Device UPS time has been changed. 0x3790 09/29/2024 09:45:48 Device UPS time has been changed. 0x3790 09/28/2024 09:45:48 Device UPS time has been changed. 0x3790 09/27/2024 09:45:49 Device UPS time has been changed. 0x3790 09/26/2024 09:45:48 Device UPS time has been changed. 0x3790 09/25/2024 09:45:48 Device UPS time has been changed. 0x3790 09/24/2024 20:55:31 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 20:54:51 Device The UPS is charging the batteries. 0x37E7 09/24/2024 20:54:31 Device Charge voltage is set to boost charge level. 0x375E 09/24/2024 20:54:31 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 20:54:31 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 09/24/2024 20:54:31 Device Mains input voltage is no longer out of tolerance. 0x3730 09/24/2024 20:54:30 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 09/24/2024 20:54:30 Device Charger is off. 0x3765 09/24/2024 20:54:30 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 09/24/2024 20:54:30 Device Mains input voltage is out of tolerance. 0x3731 09/24/2024 10:49:18 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 10:48:38 Device The UPS is charging the batteries. 0x37E7 09/24/2024 10:48:18 Device Charge voltage is set to boost charge level. 0x375E 09/24/2024 10:48:18 Device Charge voltage is set to float voltage level. 0x375C 09/24/2024 10:48:18 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 09/24/2024 10:48:18 Device Mains input voltage is no longer out of tolerance. 0x3730 09/24/2024 10:48:18 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 09/24/2024 10:48:18 Device Charger is off. 0x3765 09/24/2024 10:48:18 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 09/24/2024 10:48:18 Device Mains input voltage is out of tolerance. 0x3731 09/24/2024 09:45:48 Device UPS time has been changed. 0x3790 09/23/2024 09:45:47 Device UPS time has been changed. 0x3790 09/22/2024 09:45:49 Device UPS time has been changed. 0x3790 09/21/2024 09:45:47 Device UPS time has been changed. 0x3790 09/20/2024 09:45:48 Device UPS time has been changed. 0x3790 09/19/2024 09:45:48 Device UPS time has been changed. 0x3790 09/18/2024 09:45:49 Device UPS time has been changed. 0x3790 09/17/2024 09:45:48 Device UPS time has been changed. 0x3790 09/16/2024 09:45:47 Device UPS time has been changed. 0x3790 09/15/2024 09:45:48 Device UPS time has been changed. 0x3790 09/14/2024 09:45:48 Device UPS time has been changed. 0x3790 09/13/2024 09:45:49 Device UPS time has been changed. 0x3790 09/12/2024 09:45:47 Device UPS time has been changed. 0x3790 09/11/2024 09:45:48 Device UPS time has been changed. 0x3790 09/10/2024 09:45:48 Device UPS time has been changed. 0x3790 09/09/2024 09:45:48 Device UPS time has been changed. 0x3790 09/08/2024 09:45:48 Device UPS time has been changed. 0x3790 09/07/2024 09:45:48 Device UPS time has been changed. 0x3790 09/06/2024 09:45:47 Device UPS time has been changed. 0x3790 09/05/2024 09:45:48 Device UPS time has been changed. 0x3790 09/04/2024 09:45:48 Device UPS time has been changed. 0x3790 09/03/2024 09:45:48 Device UPS time has been changed. 0x3790 09/02/2024 09:45:48 Device UPS time has been changed. 0x3790 09/01/2024 09:45:48 Device UPS time has been changed. 0x3790 08/31/2024 14:22:42 Device Charge voltage is set to float voltage level. 0x375C 08/31/2024 14:22:02 Device The UPS is charging the batteries. 0x37E7 08/31/2024 14:21:42 Device Charge voltage is set to boost charge level. 0x375E 08/31/2024 14:21:42 Device Charge voltage is set to float voltage level. 0x375C 08/31/2024 14:21:42 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/31/2024 14:21:42 Device Mains input voltage is no longer out of tolerance. 0x3730 08/31/2024 14:21:42 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 08/31/2024 14:21:42 Device Charger is off. 0x3765 08/31/2024 14:21:42 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/31/2024 14:21:42 Device Mains input voltage is out of tolerance. 0x3731 08/31/2024 09:45:47 Device UPS time has been changed. 0x3790 08/30/2024 09:45:49 Device UPS time has been changed. 0x3790 08/29/2024 09:45:48 Device UPS time has been changed. 0x3790 08/28/2024 09:45:48 Device UPS time has been changed. 0x3790 08/27/2024 09:45:48 Device UPS time has been changed. 0x3790 08/26/2024 22:16:44 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:16:04 Device The UPS is charging the batteries. 0x37E7 08/26/2024 22:15:44 Device Charge voltage is set to boost charge level. 0x375E 08/26/2024 22:15:44 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:15:44 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/26/2024 22:15:44 Device Mains input voltage is no longer out of tolerance. 0x3730 08/26/2024 22:15:44 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 08/26/2024 22:15:44 Device Charger is off. 0x3765 08/26/2024 22:15:44 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:15:44 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/26/2024 22:15:44 Device Mains input voltage is out of tolerance. 0x3731 08/26/2024 22:15:34 Device The UPS is charging the batteries. 0x37E7 08/26/2024 22:15:14 Device Charge voltage is set to boost charge level. 0x375E 08/26/2024 22:15:14 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:15:14 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/26/2024 22:15:14 Device Mains input voltage is no longer out of tolerance. 0x3730 08/26/2024 22:15:14 Device Charger is off. 0x3765 08/26/2024 22:15:14 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:15:14 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/26/2024 22:15:14 Device Mains input voltage is out of tolerance. 0x3731 08/26/2024 22:14:54 Device Charge voltage is set to boost charge level. 0x375E 08/26/2024 22:14:54 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:14:54 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/26/2024 22:14:54 Device Mains input voltage is no longer out of tolerance. 0x3730 08/26/2024 22:14:53 Device Charger is off. 0x3765 08/26/2024 22:14:53 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:14:53 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/26/2024 22:14:53 Device Mains input voltage is out of tolerance. 0x3731 08/26/2024 22:14:53 Device Charge voltage is set to boost charge level. 0x375E 08/26/2024 22:14:53 Device Charge voltage is set to float voltage level. 0x375C 08/26/2024 22:14:53 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/26/2024 22:14:53 Device Mains input voltage is no longer out of tolerance. 0x3730 08/26/2024 22:14:52 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 08/26/2024 22:14:52 Device Charger is off. 0x3765 08/26/2024 22:14:52 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/26/2024 22:14:52 Device Mains input voltage is out of tolerance. 0x3731 08/26/2024 09:45:48 Device UPS time has been changed. 0x3790 08/25/2024 09:45:49 Device UPS time has been changed. 0x3790 08/24/2024 09:45:47 Device UPS time has been changed. 0x3790 08/23/2024 09:45:48 Device UPS time has been changed. 0x3790 08/22/2024 09:45:48 Device UPS time has been changed. 0x3790 08/21/2024 09:45:49 Device UPS time has been changed. 0x3790 08/20/2024 09:45:48 Device UPS time has been changed. 0x3790 08/19/2024 09:45:48 Device UPS time has been changed. 0x3790 08/18/2024 09:45:48 Device UPS time has been changed. 0x3790 08/17/2024 09:45:48 Device UPS time has been changed. 0x3790 08/16/2024 09:45:48 Device UPS time has been changed. 0x3790 08/15/2024 09:45:49 Device UPS time has been changed. 0x3790 08/14/2024 09:45:47 Device UPS time has been changed. 0x3790 08/13/2024 09:45:48 Device UPS time has been changed. 0x3790 08/13/2024 08:55:31 Device Charge voltage is set to float voltage level. 0x375C 08/13/2024 00:47:55 Device The UPS is charging the batteries. 0x37E7 08/13/2024 00:47:35 Device Charge voltage is set to boost charge level. 0x375E 08/13/2024 00:47:35 Device Charge voltage is set to float voltage level. 0x375C 08/13/2024 00:47:35 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 08/13/2024 00:47:35 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 08/13/2024 00:47:35 Device Battery self test is inactive. 0x37D9 08/13/2024 00:47:35 Device Battery capacity is above 75%. 0x37D5 08/13/2024 00:47:35 Device Battery self test has been completed. 0x37DC 08/13/2024 00:00:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 08/13/2024 00:00:01 Device Charger is off. 0x3765 08/13/2024 00:00:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 08/13/2024 00:00:01 Device Battery self test is running. 0x37DA 08/12/2024 09:45:49 Device UPS time has been changed. 0x3790 08/11/2024 09:45:48 Device UPS time has been changed. 0x3790 08/10/2024 09:45:48 Device UPS time has been changed. 0x3790 08/09/2024 09:45:47 Device UPS time has been changed. 0x3790 08/08/2024 09:45:48 Device UPS time has been changed. 0x3790 08/07/2024 09:45:48 Device UPS time has been changed. 0x3790 08/06/2024 09:45:48 Device UPS time has been changed. 0x3790 08/05/2024 09:45:48 Device UPS time has been changed. 0x3790 08/04/2024 09:45:48 Device UPS time has been changed. 0x3790 08/03/2024 09:45:47 Device UPS time has been changed. 0x3790 08/02/2024 09:45:49 Device UPS time has been changed. 0x3790 08/01/2024 09:45:48 Device UPS time has been changed. 0x3790 07/31/2024 09:45:48 Device UPS time has been changed. 0x3790 07/30/2024 09:45:47 Device UPS time has been changed. 0x3790 07/29/2024 09:45:48 Device UPS time has been changed. 0x3790 07/28/2024 09:45:48 Device UPS time has been changed. 0x3790 07/27/2024 09:45:48 Device UPS time has been changed. 0x3790 07/26/2024 09:45:48 Device UPS time has been changed. 0x3790 07/25/2024 09:45:48 Device UPS time has been changed. 0x3790 07/24/2024 09:45:47 Device UPS time has been changed. 0x3790 07/23/2024 09:45:49 Device UPS time has been changed. 0x3790 07/23/2024 04:48:51 Device The firmware of the Display is no longer detected as incompatible with the rest of the system. 0x3788 07/23/2024 04:48:42 Device Communication between Main Controller and display is fine. 0x370B 07/23/2024 04:48:17 Device Main Controller is unable to communicate with the display. 0x370C 07/22/2024 09:45:48 Device UPS time has been changed. 0x3790 07/21/2024 09:45:48 Device UPS time has been changed. 0x3790 07/20/2024 09:45:48 Device UPS time has been changed. 0x3790 07/19/2024 09:45:47 Device UPS time has been changed. 0x3790 07/19/2024 09:36:31 Device Charge voltage is set to float voltage level. 0x375C 07/19/2024 09:35:52 Device The UPS is charging the batteries. 0x37E7 07/19/2024 09:35:32 Device Charge voltage is set to boost charge level. 0x375E 07/19/2024 09:35:32 Device Charge voltage is set to float voltage level. 0x375C 07/19/2024 09:35:32 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 07/19/2024 09:35:32 Device Mains input voltage is no longer out of tolerance. 0x3730 07/19/2024 09:35:31 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 07/19/2024 09:35:31 Device Charger is off. 0x3765 07/19/2024 09:35:31 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 07/19/2024 09:35:31 Device Mains input voltage is out of tolerance. 0x3731 07/18/2024 09:45:49 Device UPS time has been changed. 0x3790 07/17/2024 09:45:48 Device UPS time has been changed. 0x3790 07/16/2024 09:45:48 Device UPS time has been changed. 0x3790 07/16/2024 08:59:55 Device Charge voltage is set to float voltage level. 0x375C 07/16/2024 08:59:15 Device The UPS is charging the batteries. 0x37E7 07/16/2024 08:58:56 Device Input is no longer missing a phase. 0x373C 07/16/2024 08:58:55 Device Charge voltage is set to boost charge level. 0x375E 07/16/2024 08:58:55 Device Charge voltage is set to float voltage level. 0x375C 07/16/2024 08:58:55 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 07/16/2024 08:58:55 Device Mains input voltage is no longer out of tolerance. 0x3730 07/16/2024 08:58:55 Device Mains input frequency is no longer out of tolerance. 0x3734 07/16/2024 08:58:50 Device Mains input frequency is out of tolerance. 0x3735 07/16/2024 08:58:50 Device Input is missing a phase. 0x373D 07/16/2024 08:58:49 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 07/16/2024 08:58:49 Device Charger is off. 0x3765 07/16/2024 08:58:49 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 07/16/2024 08:58:49 Device Mains input voltage is out of tolerance. 0x3731 07/16/2024 08:58:27 Device Charge voltage is set to float voltage level. 0x375C 07/16/2024 08:57:47 Device The UPS is charging the batteries. 0x37E7 07/16/2024 08:57:28 Device Input is no longer missing a phase. 0x373C 07/16/2024 08:57:27 Device Charge voltage is set to boost charge level. 0x375E 07/16/2024 08:57:27 Device Charge voltage is set to float voltage level. 0x375C 07/16/2024 08:57:27 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 07/16/2024 08:57:27 Device Mains input voltage is no longer out of tolerance. 0x3730 07/16/2024 08:57:27 Device Mains input frequency is no longer out of tolerance. 0x3734 07/16/2024 08:56:46 Device Mains input frequency is out of tolerance. 0x3735 07/16/2024 08:56:46 Device Input is missing a phase. 0x373D 07/16/2024 08:56:46 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 07/16/2024 08:56:46 Device Charger is off. 0x3765 07/16/2024 08:56:46 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 07/16/2024 08:56:46 Device Mains input voltage is out of tolerance. 0x3731 07/15/2024 09:45:48 Device UPS time has been changed. 0x3790 07/14/2024 09:45:48 Device UPS time has been changed. 0x3790 07/13/2024 09:45:48 Device UPS time has been changed. 0x3790 07/12/2024 09:45:48 Device UPS time has been changed. 0x3790 07/11/2024 09:45:47 Device UPS time has been changed. 0x3790 07/10/2024 09:45:48 Device UPS time has been changed. 0x3790 07/09/2024 09:45:48 Device UPS time has been changed. 0x3790 07/08/2024 09:45:48 Device UPS time has been changed. 0x3790 07/07/2024 09:45:48 Device UPS time has been changed. 0x3790 07/06/2024 16:10:27 Device Charge voltage is set to float voltage level. 0x375C 07/06/2024 16:09:47 Device The UPS is charging the batteries. 0x37E7 07/06/2024 16:09:28 Device Input is no longer missing a phase. 0x373C 07/06/2024 16:09:27 Device Charge voltage is set to boost charge level. 0x375E 07/06/2024 16:09:27 Device Charge voltage is set to float voltage level. 0x375C 07/06/2024 16:09:27 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 07/06/2024 16:09:27 Device Mains input voltage is no longer out of tolerance. 0x3730 07/06/2024 16:09:27 Device Mains input frequency is no longer out of tolerance. 0x3734 07/06/2024 16:09:23 Device Mains input frequency is out of tolerance. 0x3735 07/06/2024 16:09:22 Device Input is missing a phase. 0x373D 07/06/2024 16:09:22 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 07/06/2024 16:09:22 Device Charger is off. 0x3765 07/06/2024 16:09:22 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 07/06/2024 16:09:22 Device Mains input voltage is out of tolerance. 0x3731 07/06/2024 16:03:57 Device The UPS inverter output is in phase with the bypass input. 0x3721 07/06/2024 16:03:55 Device The UPS inverter output is not in phase with the bypass input. 0x3722 07/06/2024 16:03:38 Device The UPS inverter output is in phase with the bypass input. 0x3721 07/06/2024 16:03:37 Device The UPS inverter output is not in phase with the bypass input. 0x3722 07/06/2024 16:03:14 Device Charge voltage is set to float voltage level. 0x375C 07/06/2024 16:02:35 Device The UPS is charging the batteries. 0x37E7 07/06/2024 16:02:15 Device Input is no longer missing a phase. 0x373C 07/06/2024 16:02:14 Device Charge voltage is set to boost charge level. 0x375E 07/06/2024 16:02:14 Device Charge voltage is set to float voltage level. 0x375C 07/06/2024 16:02:14 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 07/06/2024 16:02:14 Device Mains input voltage is no longer out of tolerance. 0x3730 07/06/2024 16:02:14 Device Mains input frequency is no longer out of tolerance. 0x3734 07/06/2024 16:01:32 Device Mains input frequency is out of tolerance. 0x3735 07/06/2024 16:01:32 Device Input is missing a phase. 0x373D 07/06/2024 16:01:32 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 07/06/2024 16:01:32 Device Charger is off. 0x3765 07/06/2024 16:01:32 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 07/06/2024 16:01:32 Device Mains input voltage is out of tolerance. 0x3731 07/06/2024 09:45:48 Device UPS time has been changed. 0x3790 07/05/2024 09:45:48 Device UPS time has been changed. 0x3790 07/04/2024 09:45:47 Device UPS time has been changed. 0x3790 07/03/2024 09:45:48 Device UPS time has been changed. 0x3790 07/02/2024 09:45:49 Device UPS time has been changed. 0x3790 07/01/2024 09:45:48 Device UPS time has been changed. 0x3790 06/30/2024 09:45:47 Device UPS time has been changed. 0x3790 06/29/2024 09:45:48 Device UPS time has been changed. 0x3790 06/28/2024 09:45:48 Device UPS time has been changed. 0x3790 06/27/2024 09:45:48 Device UPS time has been changed. 0x3790 06/26/2024 09:45:48 Device UPS time has been changed. 0x3790 06/25/2024 09:45:48 Device UPS time has been changed. 0x3790 06/24/2024 09:45:48 Device UPS time has been changed. 0x3790 06/23/2024 09:45:48 Device UPS time has been changed. 0x3790 06/22/2024 09:45:48 Device UPS time has been changed. 0x3790 06/21/2024 09:45:47 Device UPS time has been changed. 0x3790 06/20/2024 09:45:48 Device UPS time has been changed. 0x3790 06/19/2024 09:45:48 Device UPS time has been changed. 0x3790 06/18/2024 09:45:48 Device UPS time has been changed. 0x3790 06/17/2024 09:45:48 Device UPS time has been changed. 0x3790 06/16/2024 09:45:47 Device UPS time has been changed. 0x3790 06/15/2024 09:45:48 Device UPS time has been changed. 0x3790 06/14/2024 09:45:49 Device UPS time has been changed. 0x3790 06/13/2024 09:45:48 Device UPS time has been changed. 0x3790 06/12/2024 09:45:48 Device UPS time has been changed. 0x3790 06/11/2024 09:45:48 Device UPS time has been changed. 0x3790 06/11/2024 08:54:43 Device Charge voltage is set to float voltage level. 0x375C 06/11/2024 00:47:56 Device The UPS is charging the batteries. 0x37E7 06/11/2024 00:47:36 Device Charge voltage is set to boost charge level. 0x375E 06/11/2024 00:47:36 Device Charge voltage is set to float voltage level. 0x375C 06/11/2024 00:47:36 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 06/11/2024 00:47:36 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 06/11/2024 00:47:36 Device Battery self test is inactive. 0x37D9 06/11/2024 00:47:36 Device Battery capacity is above 75%. 0x37D5 06/11/2024 00:47:36 Device Battery self test has been completed. 0x37DC 06/11/2024 00:00:01 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 06/11/2024 00:00:01 Device Charger is off. 0x3765 06/11/2024 00:00:01 Device On battery power in response to a test of the performance of the batteries. 0x3755 06/11/2024 00:00:01 Device Battery self test is running. 0x37DA 06/10/2024 09:45:48 Device UPS time has been changed. 0x3790 06/09/2024 09:45:49 Device UPS time has been changed. 0x3790 06/08/2024 09:45:47 Device UPS time has been changed. 0x3790 06/07/2024 09:45:48 Device UPS time has been changed. 0x3790 06/06/2024 09:45:48 Device UPS time has been changed. 0x3790 06/05/2024 09:45:49 Device UPS time has been changed. 0x3790 06/04/2024 09:45:48 Device UPS time has been changed. 0x3790 06/03/2024 09:45:48 Device UPS time has been changed. 0x3790 06/02/2024 09:45:48 Device UPS time has been changed. 0x3790 06/01/2024 09:45:48 Device UPS time has been changed. 0x3790 05/31/2024 09:45:49 Device UPS time has been changed. 0x3790 05/30/2024 09:45:48 Device UPS time has been changed. 0x3790 05/29/2024 09:45:48 Device UPS time has been changed. 0x3790 05/28/2024 09:45:48 Device UPS time has been changed. 0x3790 05/27/2024 09:45:47 Device UPS time has been changed. 0x3790 05/26/2024 09:45:49 Device UPS time has been changed. 0x3790 05/25/2024 09:45:48 Device UPS time has been changed. 0x3790 05/24/2024 09:45:48 Device UPS time has been changed. 0x3790 05/23/2024 09:45:48 Device UPS time has been changed. 0x3790 05/23/2024 04:18:07 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 04:17:28 Device The UPS is charging the batteries. 0x37E7 05/23/2024 04:17:08 Device Input is no longer missing a phase. 0x373C 05/23/2024 04:17:08 Device Charge voltage is set to boost charge level. 0x375E 05/23/2024 04:17:08 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 04:17:08 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/23/2024 04:17:08 Device Mains input voltage is no longer out of tolerance. 0x3730 05/23/2024 04:17:07 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 04:16:23 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 04:16:23 Device Input is missing a phase. 0x373D 05/23/2024 04:16:22 Device The phase rotation on mains input is fine. 0x3732 05/23/2024 04:16:22 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/23/2024 04:16:22 Device Charger is off. 0x3765 05/23/2024 04:16:22 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/23/2024 04:16:22 Device Mains input voltage is out of tolerance. 0x3731 05/23/2024 04:14:52 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 04:14:12 Device The UPS is charging the batteries. 0x37E7 05/23/2024 04:13:52 Device Charge voltage is set to boost charge level. 0x375E 05/23/2024 04:13:52 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 04:13:52 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/23/2024 04:13:52 Device Mains input voltage is no longer out of tolerance. 0x3730 05/23/2024 04:13:52 Device The phase rotation on input is incorrect. 0x3733 05/23/2024 04:13:51 Device Input is no longer missing a phase. 0x373C 05/23/2024 04:13:50 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 04:13:50 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 04:13:50 Device Input is missing a phase. 0x373D 05/23/2024 04:13:50 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 04:13:49 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 04:13:49 Device The phase rotation on mains input is fine. 0x3732 05/23/2024 04:13:49 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/23/2024 04:13:49 Device Charger is off. 0x3765 05/23/2024 04:13:49 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/23/2024 04:13:49 Device Mains input voltage is out of tolerance. 0x3731 05/23/2024 04:07:05 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 04:06:25 Device The UPS is charging the batteries. 0x37E7 05/23/2024 04:06:05 Device Charge voltage is set to boost charge level. 0x375E 05/23/2024 04:06:05 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 04:06:05 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/23/2024 04:06:05 Device Mains input voltage is no longer out of tolerance. 0x3730 05/23/2024 04:06:05 Device The phase rotation on input is incorrect. 0x3733 05/23/2024 04:06:05 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/23/2024 04:06:05 Device Charger is off. 0x3765 05/23/2024 04:06:05 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/23/2024 04:06:05 Device Mains input voltage is out of tolerance. 0x3731 05/23/2024 03:52:33 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 03:51:53 Device The UPS is charging the batteries. 0x37E7 05/23/2024 03:51:34 Device Input is no longer missing a phase. 0x373C 05/23/2024 03:51:33 Device Charge voltage is set to boost charge level. 0x375E 05/23/2024 03:51:33 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 03:51:33 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/23/2024 03:51:33 Device Mains input voltage is no longer out of tolerance. 0x3730 05/23/2024 03:51:33 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 03:51:28 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 03:51:28 Device Input is missing a phase. 0x373D 05/23/2024 03:51:28 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/23/2024 03:51:28 Device Charger is off. 0x3765 05/23/2024 03:51:28 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/23/2024 03:51:28 Device Mains input voltage is out of tolerance. 0x3731 05/23/2024 03:42:48 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 03:42:08 Device The UPS is charging the batteries. 0x37E7 05/23/2024 03:41:49 Device Input is no longer missing a phase. 0x373C 05/23/2024 03:41:48 Device Charge voltage is set to boost charge level. 0x375E 05/23/2024 03:41:48 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 03:41:48 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/23/2024 03:41:48 Device Mains input voltage is no longer out of tolerance. 0x3730 05/23/2024 03:41:48 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 03:41:13 Device The UPS inverter output is in phase with the bypass input. 0x3721 05/23/2024 03:41:12 Device The UPS inverter output is not in phase with the bypass input. 0x3722 05/23/2024 03:41:07 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 03:41:07 Device Input is missing a phase. 0x373D 05/23/2024 03:41:06 Device The phase rotation on mains input is fine. 0x3732 05/23/2024 03:41:06 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/23/2024 03:41:06 Device Charger is off. 0x3765 05/23/2024 03:41:06 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 03:41:06 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/23/2024 03:41:06 Device Mains input voltage is out of tolerance. 0x3731 05/23/2024 03:40:52 Device The UPS is charging the batteries. 0x37E7 05/23/2024 03:40:32 Device Charge voltage is set to boost charge level. 0x375E 05/23/2024 03:40:32 Device Charge voltage is set to float voltage level. 0x375C 05/23/2024 03:40:32 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/23/2024 03:40:32 Device Mains input voltage is no longer out of tolerance. 0x3730 05/23/2024 03:40:31 Device The phase rotation on input is incorrect. 0x3733 05/23/2024 03:40:31 Device Input is no longer missing a phase. 0x373C 05/23/2024 03:40:30 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 03:40:30 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 03:40:30 Device Input is missing a phase. 0x373D 05/23/2024 03:40:30 Device Mains input frequency is no longer out of tolerance. 0x3734 05/23/2024 03:40:29 Device Mains input frequency is out of tolerance. 0x3735 05/23/2024 03:40:28 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/23/2024 03:40:28 Device Charger is off. 0x3765 05/23/2024 03:40:28 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/23/2024 03:40:28 Device Mains input voltage is out of tolerance. 0x3731 05/22/2024 09:45:49 Device UPS time has been changed. 0x3790 05/21/2024 09:45:48 Device UPS time has been changed. 0x3790 05/20/2024 09:45:48 Device UPS time has been changed. 0x3790 05/19/2024 09:45:48 Device UPS time has been changed. 0x3790 05/18/2024 09:45:48 Device UPS time has been changed. 0x3790 05/17/2024 09:45:49 Device UPS time has been changed. 0x3790 05/16/2024 09:45:48 Device UPS time has been changed. 0x3790 05/15/2024 09:45:48 Device UPS time has been changed. 0x3790 05/14/2024 09:45:48 Device UPS time has been changed. 0x3790 05/13/2024 09:45:47 Device UPS time has been changed. 0x3790 05/12/2024 09:45:49 Device UPS time has been changed. 0x3790 05/11/2024 09:45:48 Device UPS time has been changed. 0x3790 05/10/2024 09:45:48 Device UPS time has been changed. 0x3790 05/09/2024 09:45:48 Device UPS time has been changed. 0x3790 05/08/2024 09:45:49 Device UPS time has been changed. 0x3790 05/07/2024 09:45:48 Device UPS time has been changed. 0x3790 05/06/2024 09:45:47 Device UPS time has been changed. 0x3790 05/05/2024 11:48:52 Device Charge voltage is set to float voltage level. 0x375C 05/05/2024 11:48:13 Device The UPS is charging the batteries. 0x37E7 05/05/2024 11:47:53 Device Input is no longer missing a phase. 0x373C 05/05/2024 11:47:53 Device Charge voltage is set to boost charge level. 0x375E 05/05/2024 11:47:53 Device Charge voltage is set to float voltage level. 0x375C 05/05/2024 11:47:53 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/05/2024 11:47:53 Device Mains input voltage is no longer out of tolerance. 0x3730 05/05/2024 11:47:52 Device Mains input frequency is no longer out of tolerance. 0x3734 05/05/2024 11:47:48 Device Mains input frequency is out of tolerance. 0x3735 05/05/2024 11:47:48 Device Input is missing a phase. 0x373D 05/05/2024 11:47:47 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/05/2024 11:47:47 Device Charger is off. 0x3765 05/05/2024 11:47:47 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/05/2024 11:47:47 Device Mains input voltage is out of tolerance. 0x3731 05/05/2024 11:47:36 Device Charge voltage is set to float voltage level. 0x375C 05/05/2024 11:46:56 Device The UPS is charging the batteries. 0x37E7 05/05/2024 11:46:36 Device Input is no longer missing a phase. 0x373C 05/05/2024 11:46:36 Device Charge voltage is set to boost charge level. 0x375E 05/05/2024 11:46:36 Device Charge voltage is set to float voltage level. 0x375C 05/05/2024 11:46:36 Device The load is supplied from the inverters of the unit. The UPS takes the power from the utility. 0x3750 05/05/2024 11:46:36 Device Mains input voltage is no longer out of tolerance. 0x3730 05/05/2024 11:46:36 Device Mains input frequency is no longer out of tolerance. 0x3734 05/05/2024 11:45:54 Device Mains input frequency is out of tolerance. 0x3735 05/05/2024 11:45:54 Device Input is missing a phase. 0x373D 05/05/2024 11:45:54 Device The load is drawing more power than the UPS can draw from the input, causing the UPS to draw power from the batteries. 0x37E9 05/05/2024 11:45:54 Device Charger is off. 0x3765 05/05/2024 11:45:54 Device On battery power in response to an input power problem or due to a transfer out of ECOnversion. 0x3751 05/05/2024 11:45:54 Device Mains input voltage is out of tolerance. 0x3731 05/05/2024 09:45:48 Device UPS time has been changed. 0x3790 05/04/2024 09:45:48 Device UPS time has been changed. 0x3790 05/03/2024 09:45:48 Device UPS time has been changed. 0x3790 05/02/2024 09:45:48 Device UPS time has been changed. 0x3790 05/01/2024 09:45:48 Device UPS time has been changed. 0x3790 04/30/2024 09:45:48 Device UPS time has been changed. 0x3790 04/29/2024 09:45:48 Device UPS time has been changed. 0x3790 04/29/2024 05:14:56 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 05:14:54 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 05:12:03 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 05:12:00 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 05:09:29 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 05:09:27 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 05:06:36 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 05:06:34 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 05:01:10 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 05:01:08 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 05:01:02 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 05:01:01 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 04:58:37 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 04:58:35 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 04:55:44 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 04:55:43 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 04:53:11 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 04:53:10 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 04:47:44 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 04:47:42 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 04:27:53 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 04:27:51 Device The UPS inverter output is not in phase with the bypass input. 0x3722 04/29/2024 04:24:59 Device The UPS inverter output is in phase with the bypass input. 0x3721 04/29/2024 04:24:57 Device The UPS inverter output is not in phase with the bypass input. 0x3722